Replacing honeywell stat to an other honeywell stat
I'm switching my old stat to a new one that lets me enter a program.
I have an electric central air furnace and a thermopump outside that provides heat and AC.
I'm going from a honeywell CT3600 or so (looks the same as in the manual for that one but without the program buttons) to a RTH8500.
I have 6 wires coming out of the wall and here are how they were plugged:
Green - G
Red - R
Blue - C
Orange - O/B
Yellow - W1 and jumped to Y1
White - W2 and jumped to E
My question is that on the old stat W1 is jumped with Y1 and W2 is jumped with E which means that according to the new stat I would be putting both the yellow (W1 and Y1) and the orange (O/B) in the same terminal.
How should I wire it and where should I put jumpers?
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 01:30 PM
|
|
Are the terminals on the new thermostat the same?
|
|
 |
New Member
|
|
Dec 14, 2008, 01:38 PM
|
|
The new stat has one terminal that is W and O/B with W being the conventional and O/B on the heatpump side
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 01:40 PM
|
|
Just w, no w2?
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 01:44 PM
|
|
Green wire-G
White wire- w with a jumper to E
Yellow-y
Orange-o/b
Blue-C (common)
Red-R
|
|
 |
New Member
|
|
Dec 14, 2008, 01:46 PM
|
|
Yew the terminal is marked W on the conventional side and O/B on the heat pump side. W2 for the conventional is on the aux terminal for the heat pump.
http://hvactroubleshooters.com/HONEY...%20INSTALL.pdf
On page 10 there is a nice diagram of how the new base's terminals look like
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 01:50 PM
|
|
Ok, the W terminal is also O/B (reversing valve). You're orange wire will go on that terminal,you can jumper y and w if you want. Wire it the way I listed above. Also jumper w2 and E together.
|
|
 |
New Member
|
|
Dec 14, 2008, 01:58 PM
|
|
So that means I will have the following
R - red
C - blue
G - green
W, O/B - white with a jumper to E
Orange
Y - yellow
I can jump Y and W which means on the W, O/B terminal I would end up with white, orange and yellow all being jumped with Y and E
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:01 PM
|
|
No, the jumper goes between w and y, w2 and E. White wire will go to w2 and yellow to y, orange to w..
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:05 PM
|
|
Blue-C
Yellow-y with jumper to w
Orange-W
White-W2 with jumper to E
Red-R
Green-G
|
|
 |
New Member
|
|
Dec 14, 2008, 02:06 PM
|
|
Final result would be (making sure I understand before I blow the new stat):
G, R, C in their respective terminals
White wire - E jumped to the aux, W2 terminal
Orange and yellow wires to the Y jumped to the W, O/B terminal
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:09 PM
|
|
Correct. Be sure to shut the power off to the system and double check you're work before restoring the power.
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:10 PM
|
|
That thermostat may require an installer setup,should be instructions in the book.
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:12 PM
|
|
Post back and let me know that everything worked OK, or if you have any problems.
|
|
 |
New Member
|
|
Dec 14, 2008, 02:23 PM
|
|
Heatpump switched on but it feels pretty cold. Letting it run to see if it's AC or heat.
On the old stat I would have to switch between heat for the heatpump and emergency heat for the furnace depending on how cold it was outside. Now the new stat list the available systems and I only have heat and AC as options. Will the new stat know when to switch to the furnace?
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:29 PM
|
|
You will need to set that up. This stat can be used as an heat pump or conventional, you are probably just running straight a/c right now.
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 02:34 PM
|
|
Go into the installer setup and select you're system type.
|
|
 |
New Member
|
|
Dec 14, 2008, 02:52 PM
|
|
If I should chose option 7 then when it asks me whether I have a heating or cooling changeover valve which do I enter? Try one and if it's blowing AC chose the other?
|
|
 |
Ultra Member
|
|
Dec 14, 2008, 03:34 PM
|
|
Yes, you have a reversing valve.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Trouble with honeywell stat th5220d
[ 2 Answers ]
Have heatpump gas backup when aux heat comes on it doesn't drop out the heatpump. It stays running but I'm getting 24volts from tstat?
>Moved from Forum Help<
Wiring a rth7400 honeywell Heatpump t-stat
[ 2 Answers ]
I am at my witts end with trying to wire this T-stat I am removing an old honeywell heatpump M# T874D1165 and replacing it with an RTH7400 programmable I have 7 wires running out of wall, here's what I have, BROWN and WHITE hooked to W-2 (with jumper going to Y-2) YELLOW going to...
Honeywell t-stat
[ 2 Answers ]
I have a problem. I am NOT an electrician nor do I want to be one. I have been shocked more times in my life than I can count. I just remodeled my bathroom and put in a new gfci and a hot tub and new light fixtures. I thought I would get brave and replace all of the t-stats in my house with new...
Honeywell stat to braeburn
[ 1 Answers ]
I have a honeywell stat t8734c1432. I replaced it with a braeburn 5000. I have a staights cool outside condenser and a gas furnace in the attic. I have no heat after changing the stats. The honeywell is a 4 wire stat with a jumper between the y terminal and terminal 1. white is to w, red to r,...
Amana vs honeywell stat wiring
[ 5 Answers ]
My system consists of a heatpump(amana ) / air /gas furnace.
I'm presently using an amana stat (T874tg189910574101 ) and plan on changing to a Honeywell 7400 5-1-1. The amana stat uses terminals: e jumpered to w2 with tan wire , g , c / x , r , y , and o. The honeywell diagram only shows 5 wires...
View more questions
Search
|