    Honeywell stat to braeburn
    I have a honeywell stat t8734c1432. I replaced it with a braeburn 5000. I have a staights cool outside condenser and a gas furnace in the attic. I have no heat after changing the stats. The honeywell is a 4 wire stat with a jumper between the y terminal and terminal 1. white is to w, red to r, green to g, and yellow to y.
    On my braeburn 5000 I do not have a 1 terminal or an r terminal. I do have this, rc, rh, g, w, y, b, o. If you can help me that would be great. Thanks!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 16, 2006, 06:25 AM
    Looking at the wiring diagram for a Braeburn 5000, appears you need a jumper between the Rc and Rh terminals. The red wire is the 24 volt feed to the stat, Rh feeds the heat circuit, and Rc feeds the cooling circuit, and are separate in case there is two separate power sources for heat and cool control. You only have one24 volt power source, so jump out Rc & Rh.

    FYI, the O & B terminals on the Braeburn are for heat pumps, and are not needed for your application. I cannot tell you why there is a jumper on the Honeywell stat since Honeywell makes it very difficult to find information on their products.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

T-stat not working [ 1 Answers ]

I have a digital t-stat and it went blank so I have no a/c. I ohmed all the wires leading to the t-stat and they checked out OK. I checked the secondary side of the transformer and it checks out. I changed the t-stat and it still doesn't work. There is a diode between some wires but I'm not...

Amana vs honeywell stat wiring [ 5 Answers ]

My system consists of a heatpump(amana ) / air /gas furnace. I'm presently using an amana stat (T874tg189910574101 ) and plan on changing to a Honeywell 7400 5-1-1. The amana stat uses terminals: e jumpered to w2 with tan wire , g , c / x , r , y , and o. The honeywell diagram only shows 5 wires...

Thermo stat wiring question [ 1 Answers ]

My LUX thermostat and wiring has a red wire and a white wire. My HEIL furnace is labeled R G W Y G. Does the red go to R & white to W? I'm not sure and don't want to cause any damage! Thanks for any help!

Need help with H-Well T8624D t-stat [ 5 Answers ]

I'm working at a non-profit in New York City. Recently I purchased three Honeywell T8624D's to replace our Honeywell T874D's. Then we'll have programmed on and off times and I won't have to go into each mechanical rooms to tend to the units. The wiring looks very straightforward and I tried...


View more questions Search