    Baseboard heaters not getting hot
    My apartment has five Marley C Model TA2ANWC, double thermostat, 22 amps 120-277 baseboard heaters. All are wired with 10-2 AWG.

    One double circuit breaker is marked with two 60s and the three units work fine.

    The other double circuit breaker is marked with two 50s and operates the other two baseboard heaters... BARELY!! A wall thermometer only reads 70 degrees when resting on the unit 10 minutes compared to 120 degrees of the other heaters in two minutes.

    Common sense tells me the circuit breaker is the culprit. I was taught how to replace breakers but never taught about the numbers. My out of town landlord is dragging his feet to correct the issue and we have single digit wind chill temps. I need to get the two units working.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 8, 2008, 05:08 PM
    First you need to check the ofending circuit breakers to see if they are really bad. You will need a electric meter/tester. When activated each leg of the 220 volt breaker should show 120 volts or there abouts. When jumped across the two terminals it should read 220/240 volts or there abouts.

    From your description the baseboard heaters might be operating on 120 volts so I am confused as to the exact wiring and without being there this is the best info I can give.

    If the heaters that are having a problem are heating at all it could be the circuit lost one leg of the 220 volts. It is also possible that the thermostat or limit control could be defective.

    The owner of your dwelling unit is responsible for repairs especially heat so if he does not want to fix it call a repair person pay the bill and deduct it off your next rent payment.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Baseboard Heaters [ 1 Answers ]

I am going to install some baseboard heaters in my basement and need to know how far off the floor do they get mounted or do they set right next to / on the floor? Any info on this I get is appreciated. Thanks. S N

Baseboard heaters [ 11 Answers ]

I am getting ready to put in 4 baseboard heaters 3 of them will be in one room upstairs and the other downstairs. I need help wiring them all. Let me clarify, the 3 baseboard heaters need to be wired together on one breaker and the other will be on its own breaker. Help.

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...

Baseboard heaters [ 1 Answers ]

Hello, Are there any rules for running #10 to Junction boxes in basement right below heaters and tapping off with 12/2 to them less than 6'. I'm running 30 amp circuit for 6000 watts of baseboard heat in parallel

Baseboard heaters [ 12 Answers ]

Hi all.. New to the forum.. Thanks in advance for any help.. I am trying to set up new baseboard heating in my basement.. My questions are to what size breakers to use and if I can put it all on one circuit.. I want to set up 3 rooms: Room 1 - 2 1000 watt heaters Room 2 & 3 - 1 1500 watt...


View more questions Search