    Baseboard heaters
    Hello,

    Are there any rules for running #10 to Junction boxes in basement right below heaters and tapping off with 12/2 to them less than 6'. I'm running 30 amp circuit for 6000 watts of baseboard heat in parallel
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 4, 2007, 10:33 AM
    The rule that would apply is in the NEC NFPA 70 Section 210.19 (A) (4) Exception #1 (c), limiting this tap to 18 inches.Careful placement of the junction boxes should get you close enough.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 baseboard heaters, 2 thermostats [ 5 Answers ]

I have ran a 12/2 up to a point where I want to power two 1500 (240v) watt baseboard heaters each running off a separate thermostat. Each heater will heat a separate room. I have double-pole wall-mount thermostats. Do I split my 12/2 and go to the thermostats or is there another way this should...

New to baseboard heaters [ 24 Answers ]

Hello; I need a lot of electrical help/advice. I am trying to install an electrical baseboard heater in a basement room (15'X10'). My friend helped me already do the following: Run the conduit and electrical box for thermostat Pull all the wires Mounted the baseboard heater to the wall We...

Electric baseboard heaters [ 1 Answers ]

What size wire and heatre do I need for a room size 15*11

Electric baseboard heaters [ 3 Answers ]

One of my electric baseboard heaters makes a high pitched hum when turned on to 70 degrees, unlike the others. What could be causing this and how can I fix it?

Baseboard heaters [ 12 Answers ]

Hi all.. New to the forum.. Thanks in advance for any help.. I am trying to set up new baseboard heating in my basement.. My questions are to what size breakers to use and if I can put it all on one circuit.. I want to set up 3 rooms: Room 1 - 2 1000 watt heaters Room 2 & 3 - 1 1500 watt...


View more questions Search