Nov 30, 2008, 08:42 PM
|
|
The Power Venter (aka Heat Inducer and Draft Inducer) will not start on Goodman.
FURNACE:
Made by: Goodman
Model #: GMPN080-4
THE POWER VENTER (this is what the Goodman manual calls it but other websites refer to this as the Heat or Draft Inducer):
Made by: FASCO Industries 70219565
Type: U218
Volts: 115
RPM3400
Customer Part #: B2833001S
I have been troubleshooting this all day and this is what I have learned:
The Thermostat is OK.
The Indoor Blower (Main Blower) is OK. I can turn on just the fan from the thermostat and it turns on.
Everything was working fine and then something happened. I have not moved any wires or made any changes.
Here are the sequence of events:
I turn on the heat from the thermostat.
The Thermostat clicks telling the furnace to turn on the heat.
The furnace has a humming sound coming from it. This is the Power Venter/Heat Inducer trying to turn on. The indicator light blinks three times. The panel
Explains that this means:
"Pressure switch failure to close. check venter, pressure switch, vent blockage"
The humming sound will stop and then begin again but nothing happens. Also during this time a burning smell is coming from the power venter. It smells like
Burnt plastic but I am not sure what it is.
I attempted to move the fan blades on the Power Vetner with a screw driver but the fan blades are not accessible.
My next step is to remove the Power Venter, open it up and clean it.
Any suggestions will be greatly appreciated!
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 30, 2008, 11:18 PM
|
|
You need to replace the venter motor but more than likely you will have to replace the vent motor assembly. Motor is stuck probably the bearings are bad.
|
|
 |
New Member
|
|
Dec 1, 2008, 07:43 PM
|
|
I solved it! Thanks for the feedback.
The problem was that the fan was stuck. I uninstalled the power venter and stuck my finger into the fan and dislodged whatever made the fan stick. It took quite a bit of pressure. After that it spun freely. I have no idea what was causing the fan to be stuck so hard. I reinstalled the power venter and everything works.
Does anyone know what would cause the fan to be stuck?
|
|
 |
Ultra Member
|
|
Dec 1, 2008, 07:54 PM
|
|
If this happens again in the future do the same as you did this time but I would add one thing, drill a small hole in each end of the motor, within 3/8th of an inch of where the shaft comes out. Now try to force some light weight oil into the holes you drilled. Now put it all back together,.
|
|
 |
Heating & Air Conditioning Expert
|
|
Dec 2, 2008, 02:46 AM
|
|
Glad you got it going but letmetellu's idea does work and can save your motor
|
|
 |
New Member
|
|
Dec 3, 2008, 06:18 PM
|
|
I thought I did but the problem continues to exist. This time I removed the power venter and the fan is rubbing against the case therefore there is some friction which is preventing its from spinning freely. There is enough friction to not allow it to start spinning when the thermostat asks for heat.
Any ideas how I can fix this? Can I take it somewhere and have them repair the fan. The motor and everything else is fine.
I am not certain how drilling into the motor will help. It is the fan spinning freely that is the issue.
|
|
 |
Senior Member
|
|
Dec 3, 2008, 06:22 PM
|
|
Again, you are going to need to replace the inducer assembly. When it was stuck and trying to start but failed it was most likely over amping, this can cause damage to the motor.
|
|
 |
New Member
|
|
Nov 10, 2009, 01:43 PM
|
|
I had the same smell hit mine last night. I had just recently replaced my preasure switch, but I think the Eaxhaust fan may have burned. It now shorts when I manually jump it with door open. LCD light on board does not blink, just goes off. I will take mine out and see if fan is stuck.
Any thoughts?
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 10, 2009, 02:47 PM
|
|
This post is almost a year old. LOL Start new thread.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Inducer (Draft) Motor constantly on - Lennox UHG80-100
[ 3 Answers ]
My furnace's draft motor never stops even after one full heating cycle, which it's supposed to stop!
This causes the pressure switch to stay closed even after the thermostat calls for heat the second time (after the initial heat cycle).
When I stop and start the main switch in my basement,...
Installation Procedures for draft inducer on Goodman
[ 3 Answers ]
My HVAC contractor identified that the draft inducer motor had seized on my Goodman furnace (this after he just replaced the blower motor this past April). I researched the replacement part after he gave me a quote and I would like to avoid his supplier's markup on the replacement motor, and...
Forced hot air issue (Draft inducer fan)
[ 1 Answers ]
My draft inducer fan is running for about 3 minutes before the furnace ignites. Once it ignites,the furnace is operating correctly.
This seems to be longer than normal.
Any ideas on what's wrong, or what I need to check/test?
Thanks!
No voltage to my draft inducer
[ 3 Answers ]
I have a Janitrol Furnace that will not start up.
I pulled of the tube from the draft inducer to the pressure switch. I sucked on the tube and the furnace fired up.
So I checked the voltage going to the draft inducer, it read only 6v ac.
Where do I go from here?
Goodman inducer motors
[ 3 Answers ]
Any service guys out there. I can't fiqure this one out. I just installed this 90plus furnace last yr barley used in a guest house in n.c. system ran fine never turned on just when needed for winter in the basement cause the temp in charlotte nc is warm mosly around the whole yr. went to turn...