I have a 4 year old furnace. Igniter glows but will not ignite.then it shuts down. Then starts to recyle again. I have checked voltage at the gas valve and all limit switches. All read 25 volts except one. I was told by a hvac repairman to jump it to see if it is the problem. Jumping made no difference. Im thinking it is the gas valve but can anyone suggest anything? Think twice buy once
|
|
 |
New Member
|
|
Oct 22, 2008, 05:15 PM
|
|
When do you have 25volts at the gas valve. You should only have it for a short time after the ignighter glows and no flame is detected . Check to see if you have condensate in the furnace trap. You could be losing vacuum and sucking air thus not allowing the switches to close and then open the gas valve:eek:
|
|
 |
Plumbing Expert
|
|
Oct 22, 2008, 05:26 PM
|
|
One pressure switch or two?
If you have two, the first one allows glow plug to come on, the second allows gas valve to come on. Do you ever get 24v at gas valve(as hose asked). If not then I would recommend jumping the pressure switch(the one with the rubber hose coming from the heat exchanger, not the one with the hose coming from the draft inducer). Make sure to jump the terminals after the draft inducer has stared to run. Please let me know if this helps.
|
|
 |
New Member
|
|
Oct 22, 2008, 07:45 PM
|
|
It only has one pressure switch.
|
|
 |
Plumbing Expert
|
|
Oct 23, 2008, 03:45 PM
|
|
 Originally Posted by wheeloftime
i have a 4 year old furnace. igniter glows but will not ignite.then it shuts down. Then starts to recyle again. I have checked voltage at the gas valve and all limit switches. all read 25 volts except one. i was told by a hvac repairman to jump it to see if it is the problem. jumping made no difference. Im thinking it is the gas valve but can anyone suggest anything? think twice buy once
Which one didn't read 24v? There should be a red light on your control board. What is it doing? (flashing, on steady, flash so many times fast and then so many times slow) This light is a diagnostic led and will help us figure out what is happening with your furnace. I highly doubt that it is the gas valve. There are many things to check before buying a new gas valve. I would really like to help you figure this out. Your furnace must be a 80 percenter, metal vent, not plastic?
|
|
 |
New Member
|
|
Oct 23, 2008, 03:53 PM
|
|
I have it fixed thank you. I misread one of the voltage readings on the limit switch that attatches to the squirrel cage (fan) 25 volts on one side, 56 on the other. Jumped it ran fine. Bought a new one and she's running fine so far. Now I need to re run the duct work. Existing doesn't seem to be doing the trick. Any good with that?
|
|
 |
Plumbing Expert
|
|
Oct 23, 2008, 04:06 PM
|
|
Maybe I can help, a little out of my leaque. What is the problem with existing ductwork.
|
|
 |
New Member
|
|
Oct 23, 2008, 04:42 PM
|
|
Low air flow coming out of certain vents.
No return air except for the basement. Here's a rough picture of the setup. The house was built in approx 1914.
|
|
 |
Plumbing Expert
|
|
Oct 23, 2008, 06:09 PM
|
|
Should have a return upstairs(main floor) Are you saying that you have good airflow out of some registers? Do you have adjustable supply registers?. I would start by closing down the registers that have good air flow, just a little bit.. Try to balance the system by adjusting your grills.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Goodman GMP100-3 Furnace won't Stay On.
[ 14 Answers ]
Hello,
I have a Goodman Furnace (model # GMP100-3). The furnace will not stay running. Here is the sequence of events for two different scenarios that are occurring.
Scenario 1
1. Thermostat Calls for Heat
2. Inducer starts
3. Pressure switch closes
4. Heating element glows
5. Burners...
GMH8 goodman furnace won't ignite
[ 15 Answers ]
I recently had a GMH8 goodman furnace installed in the summer and after it was installed it fired right up, but now that I don't need the air and its time to use the furnace it won't ignite. It starts to cycle but when its time to ignite the burners it shuts back off and tries to ignite again. When...
Goodman furnace won't stay lit
[ 1 Answers ]
I have a goodman furnace that goes like this.
Inducer fan comes on, 10 secs later glow lights up,
10 secs later get blue flames
10 secs later blue flames goes out. Repeats 3 times
I have replaced the flame sensor still same problem
But here is the thing. I am only getting 10 volts to the...
Goodman furnace will not lite
[ 1 Answers ]
My Goodman GMP series furnace will not lite. The inginiter glows but the burners will not lite. I am not getting the 24V to the gas valve. I can put 24V to it and all will work until the next time the thermostat call for heat and again the inginter will lite but the burners will not. You can hear...
Furnace won't lite
[ 1 Answers ]
I have a amana furnace can't get the hot surface igniter to work... igniter is new, no power to it.. control board flashes once , meaning a lockout(?)furnace will light if I use lighter... I checked all 3 overloads and pressure switch, all show good... induction fan runs as soon as power is on,...
View more questions
Search
|