    Replaced Thermostat and A/C will not kick on
    I am attempting to replace a Totaline thermostat with a Honeywell RTH6300B programmable thermostat.

    I have both Carrier A/C and gas furnaces for both zones (2).

    The units are all 3 years old.

    After replacing the thermostat on the first zone, I can only get the heat to kick on and it works fine. I try to test the A/C and the fan and cannot get either to kick on. I have made sure the circuit breakers are all on and the thermostat is set to cool with the temperature set below the current temperature and waited several minutes. I have read there is a 5 minute cool down on some systems.

    I seriously doubt I have mis-wired the 5 wire system and have removed the jumper per Honeywell instructions.

    Any ideas?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 21, 2008, 03:56 PM
    Recheck your wiring

    http://customer.honeywell.com/techli...0s/69-1717.pdf
    ajchandler's Avatar
    ajchandler Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 21, 2008, 05:22 PM
    Red wire connected to R
    White Wire connected to W
    Blue wire connected to Rc
    Yellow wire connected to Y
    Green wire connected to G

    All wires are tight. Still cannot turn fan on manually and A/C will not kick on.

    I have reviewed the manual and this website. I couldn't find out where I did anything wrong.

    Help someone?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #4

    Feb 21, 2008, 05:44 PM
    The blue wire is connected wrong, it is a common wire on the totaline and your new thermostat does not show a common, the red wire should be connected to both the "RH" and "RC" with a jumper, if the new thermostat has batteries tape off the blue wire and don't use it, if there is a "C" it would go there, Good luck, Mike
    ajchandler's Avatar
    ajchandler Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 21, 2008, 06:49 PM
    Dude you rock!!

    Everything works now. This is definitely not how the old thermostat was wired and the directions said to remove the jumper.

    Thanks a lot! You just saved me a service call and more importantly a whole lot of aggravation.

    I will definitely recommend this site.

    Just a side note. Why didn't the directions say something about this? I have replaced several thermostats in the past and never had an issue like this. I noticed the thermostats have different letters than they used too. Is there some sort of transition or standardization going on?

    Thanks again!
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #6

    Feb 23, 2008, 07:59 AM
    The new electronic thermostats are more versatile then the old ones and can be used for a variety of different systems and componets such as remote sensors , they will have more letters for wire connections and may need the perimeters adjusted in the advanced setup when you install it to tell it what type equipment you have and how you want it to operate. Good luck, Mike

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replaced thermostat - now no hear or a/c! [ 10 Answers ]

My 15-yr old thermostat has weird programming quirks that I got tired of so I bought a new one and installed it. I made sure to follow the instructions to the letter and am quite sure that the wiring was correct. However, when I turned the breakers in my main house breaker panel back on neither...

Replaced Thermostat No Heat [ 3 Answers ]

I had a friend replace my old thermostat with a new LUXPRO PDS 100 this summer and I had problems with my Frigidaire central air / heating system to work. At first it would not blow cool air and he came back and switched wire around. It work on cool fine for the last month and a half, but I now...

Replaced thermostat - no heat or a/c [ 7 Answers ]

Hello - I have an Amana a/c with gas heat Took out my old Honeywell T8195 thermostat to replace with the Lux TX1500 Wired it up as follows (Lux - color - Honeywell) RH - Red - R RC - connected to RH terminal G - Green - G Y - Yellow - Y

Have to trip thermostat switch to kick heat on [ 1 Answers ]

Sometimes (its happened three times, twice in last month) the heater is not kicking on. After we trip the fan-auto switch back and forth the heat will come on. It is an janitron thermostat-not digital--more than 6 years old. Gas furnace, also probably more than 6 years old. Could this be a...

No power after thermostat replaced [ 3 Answers ]

Ok... I know better... but since I was dealing with low voltage... I figured no harm... WRONG! :eek: I should have turned off the breaker when replacing my thermostat... enough said. I replaced my thermostat (simple comfort 3001) with a honeywell RTH6300b because the simple comfort display was...


View more questions Search