    Run a 220 line from electrical panal to an outlet
    I would like to run a 220 line from electrical panel
    Box to an outlet for a table saw.what for breakers
    And what gage wire should I use I will be about 20FT
    From panel? The saw motor is a 2hp 1 phase, runs at 3450 rpm
    And draws 10.2 amps
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jan 26, 2008, 09:00 AM
    2 # 12's(black and black, or black and red, plus green for ground.
    Also a 2 pole 20 Amp breaker to match panel.
    eleud's Avatar
    eleud Posts: 6, Reputation: 0
    New Member
     
    #3

    Jan 26, 2008, 09:25 AM
    Quote Originally Posted by realtree
    I would like to run a 220 line from electrical panel
    box to an outlet for a table saw.what for breakers
    and what gage wire should I use I will be about 20FT
    from panel? The saw motor is a 2hp 1 phase, runs at 3450 rpm
    and draws 10.2 amps
    10.2 amps is calling for a 40 amp breaker by code your only allowed to use 80% of the load so thererfore you will use a 40 amp double pole breaker and a 8 -2 wire black white ground both black and white wire gets hooked up to the 40 amp 2 pole break
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 27, 2008, 08:42 AM
    Eleud, please explain why a motor load of 10.2 amps needs a 40 amp breaker and #8 wire?

    I will explain how to size this circuit, and show that your advice is incorrect and way off base. If you were an electrical contractor bidding jobs, you won't be in business very long. Over-engineering is a dead giveaway of lack of Code and electrical theory knowledge.

    The 2 HP motor, while nameplate states 10.2 amps of running load, you must use Table 430.248 of the NEC to size the circuit size and breaker size.

    Being a motor that is cord connected, the motor should have built in thermal overload protection , so that does not need to be considered.

    Per table 430.248, a 2 HP motor is to be rated at 12 amps at 230 volts since the supply voltage is actually 240 volts.

    Circuit size is to be 125% of 12 amps, or 15 amp rated minimum, so #14 wire is allowed.

    The breaker will only be needed for short circuit protection, and can be up to the maximum of 250% of the value in Table 430.248, or 12 * 250 %= 30 amps, for a typical inverse time circuit breaker, which is what is used in every home.

    So, this motor circuit for a 2 HP 240 volt motor can be a minimum of #14 wire and be protected by a maximum of a 30 amp breaker.

    Oh oh, here we go again, a large breaker protecting a small wire!

    Any typical electrician would use #12 wire, which I would do myself, and use a 20 amp breaker, which is fine as long as this size breaker allows the motor to start. Many electricians do not know how to use Article 430 Motors, and cringe when a large breaker is used to protect a smaller wire.

    This particular motor typically would not start under any load at all, so a 20 amp breaker most likely will work fine consistently. Once the motor is started and rolling, the breaker will only see the actual 10.2 nameplate amps, and be there for any short circuit event.

    Again, I am assuming overload protection is built into the motor. If not, that is another topic, and overload protection is needed, in addition to any circuit breaker. For a motor circuit, any circuit breaker or fuse is only for short circuit protection of the circuit and device, and other devices are needed for overcurrent protection.

    Hkstroud is incorrect with his explanation of 10.2 amps being 5 amp per leg. If one were to measure the amps in both wires feeding the motor, the meter will read 10.2 amps on each wire. And the actual running load nor nameplate amps is not to be used to size a motor circuit.

    So, Realtree, the best advice you have received is from Strat, use a #12-2 cable, tape both ends of the white wire with color tape, and connect to a 20 amp 2 Pole breaker.

    If the motor fails to start using the 20 amp breaker for some reason, this will be evident by the 20 amp breaker tripping at startup, then you may go up to a 30 amp breaker on the #12 wire.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

220 range, 110 outlet [ 4 Answers ]

I have recently acquired a range that has 220 plug - the breaker box shows a double 30 amp - can I assume that that is for a range or can I convert a 110 outlet to a 220 or are there ranges that are 110. Help!

Outdoor electrical outlet keeps tripping gfci outlet [ 3 Answers ]

Until just recently my christmas decorations would light up when we plugged them into the outdoor electrical outlet. Now when we plug it in the gfci outlet in the garage keeps getting tripped and the lights won't come on. Even when we reset the gfci, once we plug in the chord it gets tripped...

110 v outlet off a 220 while maintaining 220v for a water pump [ 2 Answers ]

I have a 10-2 with ground 220 line to a water pump with no access to a 110 circuit. I need to install a 110 circuit to run a lights in the pumphouse. Can I do this by using a 1 hot lead and the ground wire as neutral to get the 110 power and then pound a ground stake in and connect the 110 ground...

2 Heaters on 1 220 line? [ 1 Answers ]

I have a 2000 Watt 220 convection heater and would like to add another one to the same wire. Can this be done? Is it the circuit breaker tripping or melting of the wire that is the danger? Thanks

How to run 220 when all I have is 110? [ 5 Answers ]

Central A/C unit went out so I purchased a large window unit to cool a combined open living - dining - kitchen floor plan only to discover that the plug is 220. And of course I have no 220 outlet where I need to put the window unit. I'm assuming that the outlet will need to be replaced in order...


View more questions Search