    Braeburn Model 1200 2 Heat Differential's?
    I have been having a lot of problems with this thermostat getting it to maintain the temperature I have set. For example I have the temp set at 72 then I set the first and second differential's both set at 2. The problem is that the temp will go down then back up, around 70-71, then I will feel cold air then warm air again. At night when the temperature drops it will run all night never getting to the level of heat that's set and most of the time remains in aux heat mode. I have the thermostat on heat (not emergency/aux) and on auto mode. The heating and cooling guy has been to my house twice, once to recharge the heat pump, the second time he replaced the heat pump. I just don't have a lot of confidence in him anymore and think the problem may be the differential settings or the thermostat needs replaced. Any answers would be greatly appreciated!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 19, 2007, 06:12 AM
    If you are trying to use a set back thermostat on a heat pump system there is the problem. Heat pumps are not known to recover very well from a set back and I suggest you just set the temp on the heat pump and let it alone.

    Here is a copy of your instructions just in case you lost or misplaced yours.
    Read the sections about temp differentials and how to adjust.
    At the university 3 years ago we did some testing on Braeburn Thermostats. They work fine if time is taken to program them correctly. Yours is a builders model and it is missing many bells and whistles.

    http://www.braeburnonline.com/pdfs/1200_manual.pdf

    There is more on this subject just use Google.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Kenmore Elite Dryer Model 110.63932102 will not heat [ 6 Answers ]

My dryer stopped heating although it runs. I confirmed I was getting 240volts at the source. I checked the continuity of the element, the thermal fuse and the thermostat and found that they were continuous. I have read that the thermistor might have something to do with it...

Wiring a Braeburn thermostat on a trane HP [ 7 Answers ]

Hi,I have a Trane HP.It is a package unit(one piece heat and cool).I am trying to wire up a Braeburn model 3000 thermostat to it.The wiring diagrams do not help.The trane is a 3 ton unit with heat strips.The wiring diagram on it shows typical wiring for a seven wire connection to thermostat.The...

Kenmore Dryer Model # 110.96591220 Won't Heat [ 5 Answers ]

Dryer won't heat and I have continuity on all the reachable parts. Not getting juice to the coil during operation. I should have 0.00 OHMS for normal operation, tested when cool on all the parts, right? Thanks for your help.:eek:

Honeywell stat to braeburn [ 1 Answers ]

I have a honeywell stat t8734c1432. I replaced it with a braeburn 5000. I have a staights cool outside condenser and a gas furnace in the attic. I have no heat after changing the stats. The honeywell is a 4 wire stat with a jumper between the y terminal and terminal 1. white is to w, red to r,...


View more questions Search