Ask Experts Questions for FREE Help !
Ask
    Kunfooki's Avatar
    Kunfooki Posts: 7, Reputation: 1
    New Member
     
    #1

    Nov 3, 2007, 07:00 PM
    Hot Tub wiring
    Hello,

    As per my post in the Hot Tub forum (https://www.askmehelpdesk.com/pools-...d-148047.html), I am working on installing a spa.

    I have already purchased 6 gauge THHN for the 130' run, but I'm beginning to second guess myself on whether that will be enough to handle this distance without a voltage drop. The tub itself is a Dimension One Chairman II.

    Also, does the THHN need to be run in conduit inside also?

    Last, do I need to run the ground the whole way, or can I use a grounding rod? Either way, does it have to be the same 6 gauge?

    Thanks!

    David
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Nov 3, 2007, 07:37 PM
    Oh, you need to post the amps or watts it will draw.
    Kunfooki's Avatar
    Kunfooki Posts: 7, Reputation: 1
    New Member
     
    #3

    Nov 3, 2007, 07:43 PM
    From what I understand from the manual, there are three operating modes... 24 Amps, 32 Amps, and 38 Amps. If I remember correctly, the sticker on the inside of the control panel says 32 amps of continuous power? It was hooked up before with about a 75 foot run the disconnect with 6 gauge, and a 15 foot run to the tub with 8 gauge... (not that that means it was right)

    Thanks,

    David
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 5, 2007, 04:18 PM
    Stick with the #6 for this run.

    All THHN must be in some sort of conduit, there are many choices from stick to flexible. And the entire run must be complete with all fittings, boxes, and supprot straps.

    The equipment ground can be min of #10, better if it was #8.

    Do not use a ground rod at the tub. Be sure to to ground all metal surrounding the tub, and an green screw in the tub controller.
    Kunfooki's Avatar
    Kunfooki Posts: 7, Reputation: 1
    New Member
     
    #5

    Nov 5, 2007, 04:58 PM
    Thanks for the advice. I just realized that I already bought the Black, White, and Green in #6 already... I don't want to mess around with the colors, so I guess I will just buy the red in 6 gauge also and not switch anything around. Hopefully my 1" PVC conduit will take nicely to four #6 wires.

    Thanks again!

    David

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a hot tub [ 1 Answers ]

The minimum wire size for my hot tub with a 40 amp GFCI is #8 gauge/4 wire, but I will have to have about 125' of wire to go from my breaker box to the hot tub. Is the rule of thumb for a wire 100' or more, to increase the size of wire to # 6 and a 50 amp GFCI ? And can I assume that I cannot...

Hot tub wiring [ 1 Answers ]

:confused: I have a hercules pro pak 733034 electric supply box for my hot tub. It has 4 wires. 2 blue and 2 black. The wires come into the contol box and the 2 blue go to a screwed connection and the one black goes to white wires in which one white wire goes to the gfi outlet on the front cover....

Wiring hot tub [ 7 Answers ]

When running wire from electrical box to hot tub should I use conduit (outdoor) or is there under ground rated 240v wire. Also what is appropriate wire size?

Wiring of a hot tub. [ 1 Answers ]

We just had a free hot tub giving to us. We already have 220 in our house. We just need some help getting it wired. It is an older Jacuzzi model. Can some one provide us with a diagram or instructions.

Hot tub wiring [ 1 Answers ]

I'm wiring a subpanel for my hot tub. I know the white wire from the breaker goes to the neutral bar, but does the neutral wire from the hot tub connect to the neutral bar or the neutral terminal on the GFI breaker?


View more questions Search