    200A. Do I have to buy special aluminum wire to bury in schedule 40 to my house?
    I need to move the meter base off my house so it will be much more convenient for me to work on the outside of the house. I want to move the meter base to the utility pole about 90 feet from the house and bury the electrical wires between the house and the pole.

    Currently, there are 3 aluminum wires that run from the step-down transformer on the utility pole to the meter base on my house.

    A guy from the electric utility said that I need to bury schedule 40 pipe in the ground and use schedule 80 on the verticals, above the ground. He said I then need to buy some special burial wire that comes with 3 wires all bundled together.

    I asked him if I could just use the aluminum wire that is already running to the house since I will be burying it inside schedule 40 pipe. He said it would not work because it would not last.

    Can someone please tell me the low down? Thanks very much.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 30, 2007, 02:45 AM
    First, once you relocate the meter to the utility pole, the main disconnect should need to be located there also. Check with the utility and the local inspector to confirm this.

    If the Main does get relocated to the pole, then 4 wires will be needed. If the Main gets to remain in the panel, and the meter alone is on the pole, then 3 wire will be sufficient.

    Local codes and condition may not allow aluminum conduit. Again check with local codes. There should be no problem with burying Al conduit, but, soil conditions, such as being close to the ocean, may corrode aluminum.

    PVC will be much cheaper and easy to install.

    If you install a complete conduit system, with elbows, fittings, etc, then I would not pull a 3 wire twisted cable, it will be too difficult to pull this cable unless the conduit is grossly oversized. I would use pulled individual conductors, aluminum wire with XHHW insulation, or copper with THHN/THWN or XHHW insulation.

    If the conduit is only used as a sleeve, and the cable will be exposed directly to earth, then you must use USE insulation. This can be individual conductors, or the multi-wire twisted cable, called URD cable.

    Word to the wise, don't just take some guy's word for anything, ask the utility for their Installation Requirements, usually published as a booklet.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I properly bury unused elcectic wire? [ 6 Answers ]

Hi, I am remodeling my bathroom. The original heating had electric baseboard. The new heating installed years ago is now oil fired forced hot air. I removed the old electric baseboard and now have an unused wire. What is the safest way of burying this wire? Thanks, Kevin

How do I cut heavy gauge aluminum stranded 220 wire? [ 2 Answers ]

I am replacing my electric range and it was connected to either a 60 or 80 amp circuit breaker that takes two slots in the panel. The wire is aluminum and both the wire in the insulation the bare wire are stranded. The insulation jackets are black and one seems to have a red stripe. The wire was...

OLD 220v Aluminum Wire Colors and meanings [ 1 Answers ]

Hi I am rewireing an outlet for my stove. 220v 30 amp service. I would like to know what the colors mean. Four wires: 1 black 1 red 1 blue? 1 twisted bare aluminium This wire is to code in my area, (Anchorage AK) I just do not know the hots and the extra ground to connect the outlet.

Hampton Bay light - aluminum wire? [ 1 Answers ]

My Hampton Bay light fixture (sku 141531) has one white and one black wire (stranded 18AWG) which are a silver color. I tried scratching to see if copper is under some coating, and cut a piece off the end to see if the end showed copper, both with no copper showing. Is there a way to confirm if the...

Junction box for #2 aluminum wire [ 3 Answers ]

I need to join a new 100A feed on #2 aluminum wire to an existing #2 wire running from the panel. So this is actually #2 alum triplex in both cases plus a #8 bare copper ground. The junction will take place in an access panel in the wall where the two PVC conduits meet. What size junction box do...


View more questions Search