Convert 220 VAC 1Phase to 2-110VAC circuits
I have a 220VAC single phase 30 amp circuit that I would like to split into two 110VAC circuits. The 220VAC circuit has 3 wires and if I measure across the two main terminals I get the 220VAC and if I measure between a main terminal and what appears to be ground, I get the 110VAC. If I take one of the wires from one of the main terminals and what appears to be the ground of the 220vac circuit then how do I get a ground for the newly created 110VAC? Can I run a separate ground from another VAC 110 outlet and connect to the new 110VAC circuit?
Thanks
|
|
|
 |
Uber Member
|
|
Nov 26, 2006, 10:58 AM
|
|
|
You should have a black, red, white, and bare or green. If so, you can do it using the white as the neutral for both circuits. It is a shortcut I don't like, but OK by code.
|
|
|
 |
Uber Member
|
|
Nov 26, 2006, 01:16 PM
|
|
|
Be sure you understand Labman correctly, he is using the proper terminology, you need a neutral AND a ground. You only mention "ground".
If the "ground" wire you have is insulated, then it can be used as a neutral. If the wire is bare it can only be a ground.
What Labman is referring to is to share a Neutral wire with two 120 volt circuits, which is allowed, but does have issues, we can get into later.
What I need from you is detail on the "ground" wire you have. Don't mean to be nitpicky, but there is a huge difference between Neutral and Ground.
Neutrals are currect carrying conductors, and if this is not correctly, or if you do not understand, you can end up sending current through-out your electrical system's grounding.
Running another wire from another outlet is never allowed. Especially if your not sure what you are running , either a ground, or a neutral.
Where are you located?
What type of cable is this wiring?
Is the "ground" insulated or bare?
I do not believe you have enough information to continue with what you are proposing until we get more detail from you.
|
|
|
 |
New Member
|
|
Nov 26, 2006, 07:08 PM
|
|
|
Thanks for the quick responses. I checked again and unfortunately it is only a 3 wire cable for the 220VAC circuit. It has a white, black and a bare ground in a orange shield. This is what has thrown me as I was expecting a 4 wire cable for the 220, two hots , a neutral and a ground. I haven't done a voltage or continuity check from the ground of the 220 and a 110 circuit to see if there is voltage between the two or if they are indeed both at ground potential. Before I did any thing I wanted to see what the experts had to say. Thanks for all the help
 Originally Posted by tkrussell
Be sure you understand Labman correctly, he is using the proper terminology, you need a neutral AND a ground. You only mention "ground".
If the "ground" wire you have is insulated, then it can be used as a neutral. If the wire is bare it can only be a ground.
What Labman is referring to is to share a Neutral wire with two 120 volt circuits, which is allowed, but does have issues, we can get into later.
What I need from you is detail on the "ground" wire you have. Don't mean to be nitpicky, but there is a huge difference bewteen Neutral and Ground.
Neutrals are currect carrying conductors, and if this is not correctly, or if you do not understand, you can end up sending current through-out your electrical system's grounding.
Running another wire from another outlet is never allowed. Especially if your not sure what you are running , either a ground, or a neutral.
Where are you located?
What type of cable is this wiring?
Is the "ground" insulated or bare?
I do not beleive you have enough information to continue with what you are proposing until we get more detail from you.
|
|
|
 |
New Member
|
|
May 15, 2018, 01:05 PM
|
|
|
I have a 220 vac line going to a GFI box for my hot tub. I want to tap off one side of my 220 vac in the box to go to a new outlet. I plan on connecting the 110 vac to either the Black wire or the Red wire Plus the White neutral wire and the Bare wire. (all before the GFI breaker.) I will then install a GFI on my 110 vac outlet.
Does that sound right?
Thanks,
Dennis
|
|
|
 |
Uber Member
|
|
May 15, 2018, 03:04 PM
|
|
|
NEC requires a dedicated circuit for a spa/hot tub. Any outlets located at the spa must be on a separate GFCI circuit.
|
|
|
 |
Uber Member
|
|
May 18, 2018, 09:36 AM
|
|
|
You need a Neutral AND Ground. Ground is Not to carry Current, If you did have a ground and Neutral, a Red and Black can Share a Neutral(a Multi Circuit), they need to Be Next to each other on Panel, Opposite phases, on a 2 Pole Breaker.
Being on opposite phases, If 1 circuit draws 20 amps, and other draws 15 amps, the Neutral carries the difference(5 amps), if they were on same phase, Neutral would carry current of both(35 Amps)
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Vac pumps
[ 5 Answers ]
Just wondering how long do you leave the pump on the condencer? For 1.5 and 2 T I usually leave the pump on for about 20 to 30 min. Yesterday and today I installed 3 - 5 tonns and 3-4 tonnes at a new building . Tomorrow I'll vac them out for about 30 min each. If you don't mind me asking, what's...
24 Volt connection on central vac
[ 1 Answers ]
I just got a brand-new Hoover central vac as a wedding present and I'm trying to connect it. The instructions are VERY vague they simply say to connect the 24 volt power in the proper space. Easier said than done... I have the rough in from my contractor and the wire looks like a phone line. It has...
24 VAC to thermostat
[ 1 Answers ]
I've got a new thermostat that needs 24VAC to run. I've seen a few Q&A's on this, I have one specific question.
OK, I removed the plate on my furnace that exposes all the electrical connections, and there's the YWGR terminals, with the appropriate colored wires attached, then there's a "C"...
46 VAC pre-wire for ceiling fan
[ 3 Answers ]
I just moved into a new home that the builder said was pre-wired for ceiling fans. I bought the first fan and light combination, but when I popped the ceiling junction box cover off and measured AC voltage between red and white or red and copper with the switch on, I only found 46 VAC. I measured...
Trying to replace a 24 vac transformer
[ 3 Answers ]
Hi Everyone,
I need instructions on how to wire the junction box where the 120 vac power, the fan limit, and the blower motor wires all come together. I undid all the wires and got confused on how to put it back together.
Here are the facts: 25 year old Rheem gas hot air upright furnace.
Three...
View more questions
Search
|