    bjbpublic's Avatar
    bjbpublic Posts: 2, Reputation: 1
    New Member
     
    #1

    Sep 3, 2007, 11:58 AM
    Shared Circuits & New Bathroom Fan
    My home was constructed around 1990. There are two full baths and one half bath. The bathroom receptacles share a dedicated 15A circuit (I have read that code now requires a 20A circuit) with a single GFCI outlet protecting all three locations. The vanity lights in all three bathrooms are on general lighting circuits shared with other rooms.

    I would like to add a new exhaust fan over the shower in the master bathroom, and the manufacturer requires GFCI protection for installation there.

    From my reading on this site, I know that I cannot (per code) tap into the existing GFCI-protected outlet since the circuit is shared between bathrooms. So, without running a new circuit back to the panel...

    (1) Is it permissible to add the fan to the existing general lighting circuit?

    (2) If so, what are my options to GFCI protect it?

    (3) If the solution uses a faceless GFCI, does it need to be visible in the bathroom, or can it be exposed in the attic?

    I'm not terribly keen on the idea of a GFCI breaker for the whole circuit due to the possibility of false tripping from other devices that don't need protection.

    Any help is greatly appreciated! Thanks...
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 3, 2007, 12:21 PM
    Yes the fan can go on the local lighting circuit, and the deadfront (faceless) GFI was exactly what I would suggest. It can be located anywhere convenient for you.
    bjbpublic's Avatar
    bjbpublic Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 3, 2007, 12:59 PM
    Quote Originally Posted by tkrussell
    Yes the fan can go on the local lighting circuit, and the deadfront (faceless) GFI was exactly what I would suggest. It can be located anywhere convenient for you.
    Wonderful -- thank you!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Correction-GFI & AFI Breakers & Shared Neutrals [ 3 Answers ]

I need to submit a correction to some advice I had furnished in the past regarding Ground Fault and Arc Fault circuit breakers being used on shared neutrals. I had in mind the typical single pole 120 volt breakers that will not work if two breakers are used for two 120 volt circuits that share a...

Shared neutrals - two circuits on 12/3 romex [ 5 Answers ]

I want to run two circuit with 12/3 Romex. Circuit #1 will be 3 light fixtures and circuit #2 will be two GFCI Receptacles. I am concerned about having shared neutral. From reading other post it is advised to splice all neutral and not use screw terminal to connect the two circuits. Also I will not...

Circuits allowed on a 15 Amp breaker - How many? [ 1 Answers ]

I just purchased a new townhome and have 13 wall outlets and 3 light switches on one 15 amp breaker. I wonder if that is within the electrical code? I have my PC, router, internet phone box, cable modem, portable a/c unit and of course other misc things such as lamps, camera and cell phone...

New bathroom circuits [ 1 Answers ]

I am remodeling my 2nd floor bathroom and adding laundry (gas dryer). I replacing old circuits with 2 new circuits. One dedicated to washer/dryer and another for one outlet, 2 vanity lights, 1 general illumination light, and for the exhaust fan/shower light. Can I make one 12/3 run from my...

Wiring circuits with smokes & lights [ 1 Answers ]

I am building my basement right now and have been reading about wiring and circuits. I thought I had everything figured out for my basement until I started looking into my lighting circuit today. I had a circuit that I thought I could easily add to, to handle my needs. I will be adding three...


View more questions Search