    Quote Originally Posted by Stratmando View Post
    abc, If I was to guess, I would think he is going to use that 1 wire to connect to the switches, in series. This would count as 1 wire, not 3.
    You can still use 2 groups of grounds and have a jumper between both wirenuts.
    Stratmando, Does the drawing I made looks like what you are suggesting?
    Attached Images
     
    abcsalem's Avatar
    abcsalem Posts: 70, Reputation: 2
    Junior Member
     
    #22

    Mar 3, 2010, 08:14 PM
    I leave it up to the pros to decide. Which drawing, on page 2 or page 3, should I go by when I am wiring my 3 switches with the 6 romex wires going into the plastic switch box? Which one pros would prefer, which one is neatest? And of course, both drawings are NEC code compliant, correct?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #23

    Mar 3, 2010, 08:17 PM

    Yes, could even just use just 2 red wire nuts, an have 6 wires in 1 and 5 wires in the other, with 3 of those wires being pigtails to the three switches. A jumper between the 2 wirenuts.
    You could just have 1 long pigtail as TK shows, and connect to the 3 switches. 2 wire nuts and a jumper was the main point.
    In your Daisey Chain, I find it easier to go from the left to the right? Your Drawings are very good.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #24

    Mar 4, 2010, 02:55 AM
    ABC, the one with one Greenie is exactly what is being done in the picture of the 3 gang box, and that picture is just some random picture I found on the net.

    Elsewhere in the Code, equipment grounds only need to be counted as one conductor in a box when calculating wire fill of a box, since they all need to be combined, somehow.

    The method of 3 Greenies, will fill the box quicker, and a deeper box will be needed. Electrically it is fine.

    If a ground wire for a switch loop went to the one switch, and that cable went out to a single fixture, or fixtures, isolated,that cable going out to the fixtures would not be grounded, since it was not combined as required in a gang box.

    IF all these cables were all EMT conduits, and since EMT conduit can be used as an equipment ground, no green or bare wire required, ALL the equipment grounds would be automatically connected by virtue of the connectors and locknuts at the gang box.

    This exception stated in Mike Holt thread:

    Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box.,

    Refers to the equipment ground of an Isolated Ground circuit, and allows it NOT to be combined with the system equipment grounding conductor, since an IG is intended to be just that, isolated.

    Disregard any mention of Isolated Ground when dealing with residential. IG ground is only for special situations dictated by certain equipment, such as sensitive electronics, medical equipment, etc.



    Keep in mind that Section 250.148 is for Continuity and Attachment of Equipment Grounding Conductors to Boxes. The first condition states that in all boxes all grounds get combined, and then A - E qualify how this connection shall be treated.

    250.148 (D) is NOT an exception to the first paragraph of 250.148.

    Since it refers to a plastic box, obviously the box does not need to be grounded, but re-iterates that each device in that box needs a connection to the equipment grounds.

    If equipment grounding conductors are not combined or otherwise all connected together at each box, this action will violate the first paragraph of 250.148, and so many others in the Code, as equipment ground is common, and all connected, or bonded, together, at each location, box, etc.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #25

    Mar 4, 2010, 07:15 AM

    All the grounds in a box connected together ensures they are all at the same potential, reducing a shock hazzard.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 fans 2 switches and 12 wires coming from ceiling [ 4 Answers ]

Thought this'd be easy, but…I could really use some help, before I burn down our new home. We just got a new home & my wife wanted ceiling fans with lights. The fans have a green ground wire, a black (fan), a white, and a striped black (light) wire. I have removed the 2 covers in the ceiling....

Finding wires/switches for outdoor lighting fixtures [ 6 Answers ]

I have these two outdoor lights on the front of my trailer, they didn't work so I put in new fixtures and they still don't work, I was wondering if there was any way to trace the wires to a switch that I might not be finding or to figure out where they go and why they are not working, I have tried...

Connecting ground wires on ceiling fans [ 2 Answers ]

I am attempting to install a ceiling fan. I have a question about attaching the ground wires. There are three ceiling wires (red, white and black). There is a green wire coming from the ceiling bracket and one from the downrod. Where do I attach the ground wires? Amateur installer

Connecting the right wires [ 4 Answers ]

I'm updating my thermostat and the one that I had is a ritetemp 8010 but the new digital thermostatRTH3100C wiring is not matching up This is the old setup! W-white Y-yellow G-green O-orange C-blue RC-red W2-brown There is also a jump wire that was with the red one and it is RH

Connecting 3 dimmer switches on one circuit [ 2 Answers ]

In my basement I have three separate single pole light switches that control the recessed lighting. These separate switches were all next to each other and somehow were interlinked with one another. I've moved these switches to one wall and put them in a three gang box, so I can control the...


View more questions Search