    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #22

    Feb 28, 2009, 02:41 PM
    Quote Originally Posted by DB414 View Post
    I know that and it is number 31 and that suggests like 10 different things, would it be easier if I named them to you
    31 means the pressure switch isn't closing or (in your case) is re-opening during a heating cycle. I would be willing to bet you have a clogged condensate trap or condensate accumulation in the exhaust vent because of a sag in a horizontal section, based on your description of the brief heating cycles and the fault code given. I'm not sure what you are expecting, but a pro would check "like 10 different things" if the service label lists them. There is only so much we can do for you with a mouse and a keyboard; but still, we are trying.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Thermostat problems or furnace problems [ 22 Answers ]

Is it possible that a thermostat operates correct all the time except when it reaches the temperature that is set doesn't maintain that temperature?:D I noticed that actually that thermostat gives a signal to the furnace but furnace doesn't turn on but that happens only when thermostat needs to...

Gas Furnace Problems [ 5 Answers ]

Here's my problem... I have a gas furnace that is relatively new, about 5 years old. It has an automatic water feeder and I have drained it and it refilled itself. The pilot light is on, and I have just changed the thermostat from the "yo-yo" to a digital one. I have tried connecting the two...

Gas furnace problems [ 16 Answers ]

I have a Tempstar 4 ton gas pack about 9 years old with a hsp igniter system,on a call for a 2 degree temperature rise the furnace mostly works OK. When the thermostat is adjusted to more than 2 degrees,the unit works good for a while and then starts to blow cold air. I have relaced the...

Gas furnace problems [ 2 Answers ]

I have a energy efficient furnace which comes on than egnites the gas than shuts down. Than it recycles and keeps doing it what do I do