    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #21

    Jan 9, 2009, 05:13 PM
    I still can't get the hot surface ignition to start up after it tries to get it too

    Check where the wires go to the board for the hot surface ignitor. During startup you should have voltage there. If you have voltage there then the ignitor is defective if no voltage present the hot surface control is probably bad.
    cyberheater's Avatar
    cyberheater Posts: 321, Reputation: 12
    Full Member
     
    #22

    Jan 10, 2009, 03:02 PM

    Okay, voltage at the control board at HSI location. Dug into the area were the two burners are to see if I could take a better look at the hot surface ignitor. It took some reading glasses to see that darn crack. So, I went out and got another, and installed it. Cleaned the sensor too.

    I had everything up and running just as it is supposed to. But, I look at the flames and there is some orange in the flame.
    Blue and even at burner contact, but as it goes up there is some orange. I let it run a bit, and it is better - but still there.

    I don't think this should be the case?? The flames stay the same blower on, or when blower is off.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #23

    Jan 10, 2009, 04:01 PM
    I don't think this should be the case??? The flames stay the same blower on, or when blower is off.

    Post a picture of what you are talking about with the flame.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #24

    Jan 10, 2009, 04:33 PM
    The orange streaks you see may just be the result of dusty combustion air.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a Tempstar Heater.The fan blows.no heat. [ 2 Answers ]

Here are the model / serial numbers... Model #... NDGE075RF01 867.768362 SERIAL #.. L912350186 My gas is on and we tried turning the thing off. My brother in law said that before there should be a clicking sound before the gas ignites... NO clicking sound... just blowing out air......

Why cold air blows out of cold air return when furnace is on [ 1 Answers ]

Why does cold air blow out of the cold air return when the furance is on?

Heat blows cold air [ 1 Answers ]

My daughter recently rented a house. The heat in the house blows cold air in two of the bedrooms and one vent in the dining room. The landlord is telling her these are return air ducts. If this is the case half of her house has no heat. Is this possible, there are what appear to be two return air...

CARRIER 58RAV Furnace Blows Cold Air-No Heat [ 1 Answers ]

I have a Carrier Model # 58RAV50-13112 Gas Furnace (fueled by propane) that isn’t working properly. It’s a holiday weekend and I’m without heat, so any help would be greatly appreciated. The furnace was operating properly throughout last winter. However, now it‘s not working. The fan runs but...


View more questions Search