    Spliting and Outlet with a 4 wire line
    I have a 4 wire line (red, black, white and bare ground) coming from my panel. It is hooked up to a double 15A breaker. It has been used for my washing machine and my effluence pump. I have installed a new pump and washer and now have to move the line. The previous pump had a switch involved in the circuit but I do not need this now.

    So my question is... Am I correct in my assumption that I can split the sockets by removing just the middle hot tab, put the red on top the top hot pole and the black on the bottom pole and then connect the ground and the neutral as usual.
    Or do I need a separate neutral and ground for both sockets.

    Thanks for you help!
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    May 22, 2014, 09:17 AM
    You have to first determine if that red wire is part of a three way switch.
    HLuc's Avatar
    HLuc Posts: 3, Reputation: 1
    New Member
     
    #3

    May 22, 2014, 09:24 AM
    Quote Originally Posted by ballengerb1 View Post
    You have to first determine if that red wire is part of a three way switch.
    Hi Thanks for your reply
    The wire comes directly from the panel.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    May 22, 2014, 09:25 AM
    The red wire does? Where in the panel is it connected?
    HLuc's Avatar
    HLuc Posts: 3, Reputation: 1
    New Member
     
    #5

    May 22, 2014, 09:34 AM
    Quote Originally Posted by ballengerb1 View Post
    The red wire does? Where in the panel is it connected?
    The red and the black are each coming from a separate 15 A breaker (this is a dual one where both 15A are connected together)

    This was set up just for the washer and pump and does not connect to anything else.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #6

    May 22, 2014, 01:11 PM
    It could be what we call in the trade a "multi-circuit". It is used by some as a way to save a little extra wire by not having to run two hots and two neutrals for separate circuits. There are some rules that apply to doing this. 1) the breakers must be on opposite phases in the panel. 2)they should be adjacent with a common handle that trips both breakers if one is tripped. 3)at the first place of use the whites must be tied together- not depending on the device for the connection. I imagine they decided they needed two circuits and this was the fix for it.

    FYI. If two legs or of power of different potentials or phases share a common neutral, the neutral load only carries the difference between the loads of the hot legs, which allows the neutral to be common to both circuits without the worry of overloading the neutral. If you don't correctly install the breakers on opposite legs then the neutral current is additive and you can overload the neutral. The code requires the neutrals for each circuit be split at the first point of use and stay that way. They cannot be dependent on the device for this connection. The reason for this is if you disconnect the neutral that is common to both circuits, the circuits no longer have a neutral connection and the current flows from one leg through the other leg and can potentially put close to 240 volts on a 120 volt device, which would probably burn it up. I don't care for this method myself, but it does have its place and is legal in the code. I question that it will continue to be used in house wiring due to the nature of the increased requirements for GFCI and AFCI breakers needing the neutral for the hot at the breaker and the multi-circuit method only returns one neutral for two circuits.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #7

    May 23, 2014, 05:17 AM
    "So my question is... Am I correct in my assumption that I can split the sockets by removing just the middle hot tab, put the red on top the top hot pole and the black on the bottom pole and then connect the ground and the neutral as usual."
    Yes...

    Or do I need a separate neutral and ground for both sockets."
    No...

    (in the interest of simple answers...)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I am trying to install a 3 wire welder to a drye outlet. Does the ground wire go toL [ 3 Answers ]

I am trying to install a 3 wire welder to a drye outlet. Does the ground wire go to The "L" shaped prong and the ehite and black wire to the angles flat prongs ?

How to wire a 2, 3 wire and 1, 2 wire box with a switch and outlet? [ 1 Answers ]

How do I wire a gang box with a switch? I have two 3-wire 14-3 wires feeding the box and a 2-wire 12-2 going to and outlet I want on the switch?

How do I connect a 240 VAC 4-wire generator cable to a 3-wire dryer outlet? [ 1 Answers ]

I have a 5000 watt generator that I want to hook up to power my well and some lights and refrigerator for the next couple of days until power is restored. The generator has a 240 volt outlet which I have a plug and cable for. The cable ends in 4 wires: black, red, green white. The dryer outlet and...

Al wire on old trailer home, 120v on breaker but 50v on hot wire to outlet. [ 2 Answers ]

Al wire on old trailer home, 120v on breaker but 50v on hot wire to outlet.


View more questions Search