    Intertherm furnace troubleshooting
    Intertherm furnace model E2EB-012HA will heat normally for awhile then quit. I will wake up or come home to cold house. Thermostat will show that unit should be heating but nothing is running. Thermostat shows heat running but nothing is and temperature in house is below the setting. I have turned off breaker for ten seconds and then back on. This will start the furnace and run OK for awhile then happens again. I replaced breaker thinking it might be weak but still acts the same with new breaker. Thinking it might be sequencer but not sure.

    [email protected]
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Dec 16, 2012, 01:27 PM
    You are going to have to try this while the furnace is not running yet the thermostat is calling for heat.

    Install a jumper between terminals R & W on the furnace (where the thermostat wires connect). If the furnace starts, you have a problem with either the stat or wiring.
    ryanporter's Avatar
    ryanporter Posts: 8, Reputation: 1
    New Member
     
    #3

    Dec 16, 2012, 02:57 PM
    Should I install the jumper without turning breaker or power off? I'm thinking yes, because if I turn off power then it will just react the way it has when I've shut it off before and won't know if it was the jumper that fixed it or just resetting power.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #4

    Dec 16, 2012, 07:55 PM
    You are correct. The jumper should be installed without breaking the power to the furnace.
    ryanporter's Avatar
    ryanporter Posts: 8, Reputation: 1
    New Member
     
    #5

    Dec 20, 2012, 07:47 AM
    Quote Originally Posted by Grady White View Post
    You are correct. The jumper should be installed without breaking the power to the furnace.
    Jumper wire did not start furnace, so what does that mean now?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Dec 20, 2012, 05:52 PM
    Is this a gas or electric furnace?
    ryanporter's Avatar
    ryanporter Posts: 8, Reputation: 1
    New Member
     
    #7

    Dec 21, 2012, 06:45 AM
    Quote Originally Posted by mygirlsdad77 View Post
    Is this a gas or electric furnace?
    Electric
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #8

    Dec 21, 2012, 04:54 PM
    Oh, sorry, I don't see many electric furnaces in my area so I don't have much info for you here. I will say that the few I have worked on (probably less than a dozen) have all been burned out elements or faulty sequencers, but of course there is much more to them than that. Please let me know what you find, and hopefully one of the other pros here can point you in the correct trouble shooting direction.
    ryanporter's Avatar
    ryanporter Posts: 8, Reputation: 1
    New Member
     
    #9

    Dec 21, 2012, 07:50 PM
    Quote Originally Posted by mygirlsdad77 View Post
    Oh, sorry, I dont see many electric furnaces in my area so I dont have much info for you here. I will say that the few I have worked on (probably less than a dozen) have all been burned out elements or faulty sequencers, but of course there is much more to them than that. Please let me know what you find, and hopefully one of the other pros here can point you in the correct trouble shooting direction.
    That's what I was thinking either element or sequencer. I think I will try sequencer first since it's the least expensive. Thanks for trying to help!
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #10

    Dec 23, 2012, 03:01 PM
    Yes, I would suggest the sequencer first also. A bad element would not work intermitantly, but a sequencer often times will.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Intertherm furnace troubleshooting [ 11 Answers ]

Having problems with our intertherm lp furnace. It runs for a while and then it kicks out the high limit reset on the purge blower fan. Then we shut the furnace off and reset the high limit switch button on, and it comes on again. We currently have the thermostat set at 67, if we increase the...

Intertherm furnace troubleshooting [ 0 Answers ]

1986 intertherm electric furnace<only blowing cool air on heat setting. I inspected the heat coils and they don't look broken

Troubleshooting a Intertherm Furnace [ 1 Answers ]

I have an Intertherm furnace model mmha056aahr05. Glow plug lights burner starts then shuts down. 3 blinking lights on the code says gas valve error or false flame sensed. Any ideas on problem solving or where can I get a manual Thank You

Intertherm furnace troubleshooting? [ 0 Answers ]

I have an intertherm gas furnace.. For some reason the heat portion won't kick on when turned on all gas connections and switches are on that need to be... When I bought the mobile home the original owners said that the heater worked... Any ideas why the pilot light won't kick on its fairly brand...

Intertherm furnace troubleshooting [ 2 Answers ]

My intertherm #e2eb-01sha electric furnace mostly just blows cold air. Sometimes however the heat works just fine. Also, anytime the blower is not running the furnace is hot so we have to turn off the safety disconnect. We have tried replacing the thermostat to no avail. Help please Michael