    What size ser cable for 100 amp service
    What gauge al ser do I need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #2

    Aug 9, 2012, 06:43 PM
    How far is the run? And what is the breaker on the genset rated? And you need to run control wires as well. What model generator do you have?
    wg cahill's Avatar
    wg cahill Posts: 13, Reputation: 1
    New Member
     
    #3

    Aug 13, 2012, 01:09 PM
    About 80 feet 200 # nexis smart switch. Generac 14 kw natraul gas home depot # 6052
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Aug 13, 2012, 04:34 PM
    Quote Originally Posted by wg cahill View Post
    what gauge al ser do i need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.?
    Is it 9kW or 14kW?
    And did you even begin to read the instructions?
    wg cahill's Avatar
    wg cahill Posts: 13, Reputation: 1
    New Member
     
    #5

    Aug 14, 2012, 03:19 PM
    Wrong post stan
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Aug 14, 2012, 03:28 PM
    Quote Originally Posted by wg cahill View Post
    wrong post stan
    In the orignsl post you say 9000 watts. Then in post #3 you say "generac 14 kw natraul gas home depot # 6052"
    Which one is it?
    wg cahill's Avatar
    wg cahill Posts: 13, Reputation: 1
    New Member
     
    #7

    Aug 15, 2012, 09:47 AM
    Sorry post #3 14kw is the unit.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Aug 15, 2012, 11:28 AM
    I would run a #2 aluminum 4 wire SER cable, assuming this SER cable is not installed underground in a conduit.
    wg cahill's Avatar
    wg cahill Posts: 13, Reputation: 1
    New Member
     
    #9

    Aug 15, 2012, 07:51 PM
    Would terminate in junction box on out side wall (use) #2 installed in 1.25 pvc under ground conduit to generater.
    wg cahill's Avatar
    wg cahill Posts: 13, Reputation: 1
    New Member
     
    #10

    Aug 16, 2012, 07:04 PM
    Quote Originally Posted by mike 165278 View Post
    How far is the run? And what is the breaker on the genset rated? And you need to run control wires as well. What model generator do you have?
    80 feet generac 6052 with 200# smart switch 15 feet of feeder to house will run under ground. House has 200# under ground feed panel in basement.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #11

    Aug 16, 2012, 07:45 PM
    Quote Originally Posted by wg cahill View Post
    80 feet generac 6052 with 200# smart switch 15 feet of feeder to house will run under ground. house has 200# under ground feed panel in basement.
    I would sleeve #2 XHHW in the 1 1/4 PVC, use an LB to get into the house (looks better, and much cheaper than a PVC junction box). Nipple through the wall into a 6 X 6 X 4 metal junction box, then run the 2/3 SER over to the transfer switch.

    Check the oil before you start the unit. Make sure you run another pvc pipe in the trench for the control wiring.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #12

    Aug 16, 2012, 07:49 PM
    Quote Originally Posted by mike 165278 View Post
    I would sleeve #2 XHHW in the 1 1/4 PVC,
    I recommend a supply house over a big box store. Make sure the #2 XHHW is type XHHW-2
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #13

    Aug 17, 2012, 02:46 AM
    The USE type insulation mentioned is fine also.

    I would stay with PVC fittings and junction box. Any metal fittings or junction box used in a PVC and non-metallic system will need to be grounded by the equipment grounding conductor.

    Be sure to run 4 conductors, 3 -#2 and minimum of #6 insulated for the equipment ground.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #14

    Aug 17, 2012, 05:39 AM
    Quote Originally Posted by tkrussell View Post
    The USE type insulation mentioned is fine also.

    I would stay with PVC fittings and junction box. Any metal fittings or junction box used in a PVC and non-metallic system will need to be grounded by the equipment grounding conductor.

    Be sure to run 4 conductors, 3 -#2 and minimum of #6 insulated for the equipment ground.
    Good call on keeping it all PVC.

    You can use USE, XHHW-2, URD quadplex. If you go copper, you can use THHN/THWN
    wg cahill's Avatar
    wg cahill Posts: 13, Reputation: 1
    New Member
     
    #15

    Aug 18, 2012, 05:23 PM
    Quote Originally Posted by mike 165278 View Post
    Good call on keeping it all PVC.

    You can use USE, XHHW-2, URD quadplex. If you go copper, you can use THHN/THWN
    What is the correct way to terminate the seu to the quadplex in side the plastic jun box. Home depot says to use spliceing terminals then cover with shrink wrap.
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #16

    Aug 18, 2012, 06:04 PM
    I'd use a #2 split bolt, (burndy), make sure it is dual rated cu/al then wrap it in tape. Or some NSI Polaris lugs, then you don't have to tape it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

What size wire for 220v 100 amp service at 100 feet [ 7 Answers ]

I am running 220v 100 ft to a 125 amp sub panel. A welder would be the heaviest thing used. (around 200 amp welder) what size copper wire would I need running in pvc underground

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.

200 amp service 4/0 ser cable in 2" conduit? [ 1 Answers ]

What should I run from my disconnect switch to my panel box inside for my 200 amp service. I have 2" PVC ran from the disconnect to the panel. I thought about using 4/0 SER but then read somewhere that you are not suppose to put it in conduit because of possible temp problems? Is this correct or...


View more questions Search