What gauge al ser do I need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.
![]() |
What gauge al ser do I need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.
How far is the run? And what is the breaker on the genset rated? And you need to run control wires as well. What model generator do you have?
About 80 feet 200 # nexis smart switch. Generac 14 kw natraul gas home depot # 6052
Wrong post stan
Sorry post #3 14kw is the unit.
I would run a #2 aluminum 4 wire SER cable, assuming this SER cable is not installed underground in a conduit.
Would terminate in junction box on out side wall (use) #2 installed in 1.25 pvc under ground conduit to generater.
I would sleeve #2 XHHW in the 1 1/4 PVC, use an LB to get into the house (looks better, and much cheaper than a PVC junction box). Nipple through the wall into a 6 X 6 X 4 metal junction box, then run the 2/3 SER over to the transfer switch.
Check the oil before you start the unit. Make sure you run another pvc pipe in the trench for the control wiring.
The USE type insulation mentioned is fine also.
I would stay with PVC fittings and junction box. Any metal fittings or junction box used in a PVC and non-metallic system will need to be grounded by the equipment grounding conductor.
Be sure to run 4 conductors, 3 -#2 and minimum of #6 insulated for the equipment ground.
I'd use a #2 split bolt, (burndy), make sure it is dual rated cu/al then wrap it in tape. Or some NSI Polaris lugs, then you don't have to tape it.