Aug 9, 2012, 06:28 PM
|
|
What size ser cable for 100 amp service
What gauge al ser do I need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.
|
|
|
Junior Member
|
|
Aug 9, 2012, 06:43 PM
|
|
How far is the run? And what is the breaker on the genset rated? And you need to run control wires as well. What model generator do you have?
|
|
|
New Member
|
|
Aug 13, 2012, 01:09 PM
|
|
About 80 feet 200 # nexis smart switch. Generac 14 kw natraul gas home depot # 6052
|
|
|
Electrical & Lighting Expert
|
|
Aug 13, 2012, 04:34 PM
|
|
Originally Posted by wg cahill
what gauge al ser do i need to run from a 9000 watt stand by gen to a 200 amp auto transfer switch and is this all the wireing that runs from gen to service panel in house.?
Is it 9kW or 14kW?
And did you even begin to read the instructions?
|
|
|
New Member
|
|
Aug 14, 2012, 03:19 PM
|
|
Wrong post stan
|
|
|
Electrical & Lighting Expert
|
|
Aug 14, 2012, 03:28 PM
|
|
Originally Posted by wg cahill
wrong post stan
In the orignsl post you say 9000 watts. Then in post #3 you say "generac 14 kw natraul gas home depot # 6052"
Which one is it?
|
|
|
New Member
|
|
Aug 15, 2012, 09:47 AM
|
|
Sorry post #3 14kw is the unit.
|
|
|
Uber Member
|
|
Aug 15, 2012, 11:28 AM
|
|
I would run a #2 aluminum 4 wire SER cable, assuming this SER cable is not installed underground in a conduit.
|
|
|
New Member
|
|
Aug 15, 2012, 07:51 PM
|
|
Would terminate in junction box on out side wall (use) #2 installed in 1.25 pvc under ground conduit to generater.
|
|
|
New Member
|
|
Aug 16, 2012, 07:04 PM
|
|
Originally Posted by mike 165278
How far is the run? And what is the breaker on the genset rated? And you need to run control wires as well. What model generator do you have?
80 feet generac 6052 with 200# smart switch 15 feet of feeder to house will run under ground. House has 200# under ground feed panel in basement.
|
|
|
Junior Member
|
|
Aug 16, 2012, 07:45 PM
|
|
Originally Posted by wg cahill
80 feet generac 6052 with 200# smart switch 15 feet of feeder to house will run under ground. house has 200# under ground feed panel in basement.
I would sleeve #2 XHHW in the 1 1/4 PVC, use an LB to get into the house (looks better, and much cheaper than a PVC junction box). Nipple through the wall into a 6 X 6 X 4 metal junction box, then run the 2/3 SER over to the transfer switch.
Check the oil before you start the unit. Make sure you run another pvc pipe in the trench for the control wiring.
|
|
|
Junior Member
|
|
Aug 16, 2012, 07:49 PM
|
|
Originally Posted by mike 165278
I would sleeve #2 XHHW in the 1 1/4 PVC,
I recommend a supply house over a big box store. Make sure the #2 XHHW is type XHHW-2
|
|
|
Uber Member
|
|
Aug 17, 2012, 02:46 AM
|
|
The USE type insulation mentioned is fine also.
I would stay with PVC fittings and junction box. Any metal fittings or junction box used in a PVC and non-metallic system will need to be grounded by the equipment grounding conductor.
Be sure to run 4 conductors, 3 -#2 and minimum of #6 insulated for the equipment ground.
|
|
|
Junior Member
|
|
Aug 17, 2012, 05:39 AM
|
|
Originally Posted by tkrussell
The USE type insulation mentioned is fine also.
I would stay with PVC fittings and junction box. Any metal fittings or junction box used in a PVC and non-metallic system will need to be grounded by the equipment grounding conductor.
Be sure to run 4 conductors, 3 -#2 and minimum of #6 insulated for the equipment ground.
Good call on keeping it all PVC.
You can use USE, XHHW-2, URD quadplex. If you go copper, you can use THHN/THWN
|
|
|
New Member
|
|
Aug 18, 2012, 05:23 PM
|
|
Originally Posted by mike 165278
Good call on keeping it all PVC.
You can use USE, XHHW-2, URD quadplex. If you go copper, you can use THHN/THWN
What is the correct way to terminate the seu to the quadplex in side the plastic jun box. Home depot says to use spliceing terminals then cover with shrink wrap.
|
|
|
Junior Member
|
|
Aug 18, 2012, 06:04 PM
|
|
I'd use a #2 split bolt, (burndy), make sure it is dual rated cu/al then wrap it in tape. Or some NSI Polaris lugs, then you don't have to tape it.
|
|