    Ground connection
    Have a neighbor that changed the wiring on well pump (3 wire). He ran 3 conductor to pump and no ground. He states that the water will be his ground? Is this possible to wire the pump that way?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 7, 2011, 09:00 AM
    No,

    Quote Originally Posted by Nitro2 View Post
    He states that the water will be his ground? Is this possible to wire the pump that way?
    Cannot use the metal water line as an equipment ground.

    The feeder to the pump is 3 wire, only two are the live 240 volts, the third is intened to act as the equipment ground.

    Unless the pump needs 3 wire to oeprate, that I am not aware of.
    Nitro2's Avatar
    Nitro2 Posts: 6, Reputation: 1
    New Member
     
    #3

    Sep 7, 2011, 09:09 AM
    Yes the pump is a 3 wire and has a control box he blew his capacitor twice now. The 3 wires he is running down to the pump are the 2 hot and the control. He did not run a ground wire, the pump hangs in the lake a he said he was told that the lake will be his ground?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Sep 7, 2011, 09:13 AM
    Nope, still will not work.

    The purpose of an equipment ground that comes from the power source is to insure the fault current returns to the source, in a low impedance path, to facilitate the overcurrent device, AKA circuit breaker or fuse, to open quickly in the event of a fault.

    Can you provide a datasheet of the pump motor and control so I can see why 3 branch circuit conducotrs are needed?
    Nitro2's Avatar
    Nitro2 Posts: 6, Reputation: 1
    New Member
     
    #5

    Sep 7, 2011, 09:14 AM
    Is this why he keeps blowing capacitors?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Sep 7, 2011, 09:16 AM
    Could be. All depends on how these 3 wires are connected.

    A datasheet will be helpful to learn what is there and how it is to be connected.
    Nitro2's Avatar
    Nitro2 Posts: 6, Reputation: 1
    New Member
     
    #7

    Sep 7, 2011, 09:18 AM
    Pump is 5 years old and I do not think he has them, I'll ask when I see him tonight. He bought a new capacitor and a well wire kit and wants me to drop by.
    Nitro2's Avatar
    Nitro2 Posts: 6, Reputation: 1
    New Member
     
    #8

    Sep 7, 2011, 09:21 AM
    They way he has them wired is come off pressure switch to control box, the wires out of the control box runs down to pump and red to red, black to black and third wire to yellow on pump, ground on pump cut an just hanging...
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #9

    Sep 7, 2011, 09:22 AM
    The datasheet should be available on the internet if you can provide the manufacturer and model number of the unit.
    Nitro2's Avatar
    Nitro2 Posts: 6, Reputation: 1
    New Member
     
    #10

    Sep 7, 2011, 09:25 AM
    Pump covered with algae will look for it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground connection [ 1 Answers ]

Is crimping ground wires required in receptacles now instead of twisting and using a wire tie?

Ground wire to neutral bus connection in breaker box? [ 5 Answers ]

In preparation of wiring a hot tub I took off my breaker box panel face plate and noticed that the 8-2 w/g white romex coming into my breaker box had the bare ground wire connected to the neutral bus. The other two hot wires go to the 30 amp breaker. This romex comes from my air cond compressor...

Ground connection [ 3 Answers ]

Hi I'm checking to make sure I'm not seeing things or missing something... In my current electrical panel (which I'm about to upgrade) I have the neutral and ground bars tied together with a bar. This panel is the original and is probably 10+ years old. Coming from the meter housing...

Ground wire connection for OLD wiring [ 1 Answers ]

Hello, I wired up my basement with new wiring but hooked it in to old wire supply that is in a metal case and only has two wires. IS there anyway to make the ground wore in the new wiring functional? Also, when wiring the outlets, I tire the ground wire to the metal box as I was supposed to in...

Neutral and Ground share the same connection? [ 1 Answers ]

I have a question regarding wiring for my Hot Springs Spa. The spa comes with a subpanel for two GFCI breakers, one 20-amp and one 30-amp. I have 220 wired to an existing subpanel located right next to my spa location. The only difference between my sub panel and the wiring diagram on the spa...


View more questions Search