    Replacement ceiling fan wiring
    We have a Skylark dimmer switch. Coming from the ceiling we have a blue wire, black wire, white wire, no ground that we can see.

    We had a fan with a light kit that was connected black to black, white to white, blue to blue.

    We swapped out our old fan for a new "5 minute" (ha!) Hunter fan. Hunter fan has black, black and white striped and white wires plus a ground.

    We connected black to black, black striped to blue, white to white and ground to ground on ceiling plate. Resulting in the fan working and light kit NOT working. Fan was working off the dimmer and you could lower the speed of the fan via the slide of the skylark slide. Not good.

    So we then tried

    Black to blue, black striped to black, white to white and ground to ground on ceiling plate. Results - fan doesn't work. Light kit works as desired, able to dim the light via the slide of the skylark slide.

    Of course we want both the fan and the light kit to work. We want the light kit to be dimmable and the fan to be on/off (via chain and on/off switch of Skylark).

    Any ideas? The old fan was a piece of junk but it did work as desired.

    Thanks in advance,
    M
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    May 25, 2009, 08:26 PM

    You have strange color wires. Are you Canadian? Pull the switch and tell us what wires and connections you have there. One of the two connections you tried should have worked, assuming the old fan worked properly
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    May 25, 2009, 08:31 PM
    Oops. Just reread you post. Fan will not be on/off by switch unless Skylark is special switch with multiple output terminals.
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #4

    May 25, 2009, 08:36 PM

    How did the old fan/light work? Did the slide dimmer only work the lights and not the fan?
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #5

    May 25, 2009, 08:40 PM
    Quote Originally Posted by hkstroud View Post
    You have strange color wires. Are you Canadian? Pull the switch and tell us what wires and connections you have there. One of the two connections you tried should have worked, assuming the old fan worked properly
    Thank you for your reply.

    We're in New Jersey. The old fan did work. Both fan and light worked. Light was dimmable, fan did not lessen in intensity.

    Love the new fan but right now it's hooked up black to black, black striped to blue and white to white and the light doesn't work and the fan intensifies when you slide the dimmer switch down (one expect the light to dim).
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #6

    May 25, 2009, 08:44 PM
    Quote Originally Posted by jerro View Post
    How did the old fan/light work? Did the slide dimmer only work the lights and not the fan?
    Yes, with the old fan the slide only dimmed the lights. Did nothing to the fan. Only the on/off effected the fan as one would expect.

    Old fan had black/blue/white wires which were connected to the switches black/blue/white wires.

    Hunter is funky and they have black/striped/white wires. We THOUGHT that the striped would be the 'blue' but when we connected black to black, striped to blue and white to white the fan works, light does not. Strangely when you move to dimmer slide downward the fan goes faster.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #7

    May 25, 2009, 09:23 PM

    I take it that down should dim the light. I think something went funky in the switch. Pull switch and tell what connections you have.
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #8

    May 26, 2009, 06:59 AM
    Quote Originally Posted by hkstroud View Post
    I take it that down should dim the light. I think some went funky in the switch. Pull switch and tell what connections you have.
    Very weird. Pulled the switch. Two black wires coming off the Skylark switch - one twisted to a red wire from the wall junction box and capped, the other twisted to a white wire from the wall junction box and capped. Also in that box - two more white wires and two more black wires - both of which are capped off in the box (connected to nothing).

    Note the distinct absence of a blue wire which you'll remember I have coming from the ceiling junction box (no red wire coming from ceiling junction box).

    The house is in NJ and was built in 1966. We did not install the dimmer switch or the previous fan. This fan install is the first time we are messing with this particular box. We've swapped out fans in this house before without issue but this one is proving to be a real pain.

    Thanks in advance for your advice on how to proceed.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    May 26, 2009, 07:25 AM

    By capped I take it that you mean connected together with a wire nut. If I understand correctly the diagram below is what you have in the switch box.
    Attached Images
     
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #10

    May 26, 2009, 07:28 AM
    Quote Originally Posted by hkstroud View Post
    By capped I take it that you mean connected together with a wire nut. If I understand correctly the diagram below is what you have in the switch.
    Yes, exactly. Your diagram is spot on.
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #11

    May 26, 2009, 07:43 AM
    Quote Originally Posted by nojobtakesjust5 View Post
    Yes, exactly. Your diagram is spot on.
    Note though that underneath the slide for the dimmer is an on off (left/right). This probably does not matter but just in case... Picture of switch here:

    ANTOnline.com - Lutron S-600H-IV Lutron Electronics Skylark Dimmer, Ivory #S600H-IV
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #12

    May 26, 2009, 08:29 AM

    Ok. There is only two terminals (wires) on that switch right?
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #13

    May 26, 2009, 08:35 AM
    Quote Originally Posted by hkstroud View Post
    Ok. There is only two terminals (wires) on that switch right?
    Yes
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #14

    May 26, 2009, 09:13 AM

    The switch only has one circuit. It cannot control the light and the fan independently.
    You have some funky wiring. Some where the red and white are changing to black. Is there an attic above this room where a junction box may have been installed.

    I am having a problem determining where the power source is. If the switch is wired as described, it is not at the switch. If it is in the ceiling box there must be another wire there.

    In the ceiling we know that the white is the neutral simply because you must have a neutral. Either the black or the black strip would be the power in. That wire would be hot all the time and not controlled by the switch. The other wire would be the switch leg to the switch (changing to either red or white). But, you need another wire coming back from the switch.
    Are you certain there is not another wire in the ceiling box.
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #15

    May 26, 2009, 11:02 AM
    Quote Originally Posted by hkstroud View Post
    The switch only has one circuit. It cannot control the light and the fan independently.
    You have some funky wiring. Some where the red and white are changing to black. Is there an attic above this room where a junction box may have been installed.

    I am having a problem determining where the power source is. If the switch is wired as described, it is not at the switch. If it is in the ceiling box there must be another wire there.

    In the ceiling we know that the white is the neutral simply because you must have a neutral. Either the black or the black strip would be the power in. That wire would be hot all the time and not controlled by the switch. The other wire would be the switch leg to the switch (changing to either red or white). But, you need another wire coming back from the switch.
    Are you certain there is not another wire in the ceiling box.
    Rechecked the switch box - no additional wires it is as you diagrammed previously.

    There is an attic above where the fan is installed. The attic has flooring nailed down in most of it but I'll try to see if I can find the box. Once I saw the wires in the wall I knew we'd end up needing to poke around in the attic as somewhere along the way we lost a red wire (in switch box) and gained a blue and black wire (in ceiling box).
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #16

    May 26, 2009, 11:13 AM

    OK, check fan ceiling box for an additional wire. Has to have four wires, a neutral, a hot, a wire to switch and a wire from the switch. Otherwise you have to have a junction box wired that way with a neutral, an unswitched and a switched wire from junction box to fan ceiling box. Just has to be.
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #17

    May 26, 2009, 04:31 PM
    Quote Originally Posted by hkstroud View Post
    OK, check fan ceiling box for an additional wire. Has to have four wires, a neutral, a hot, a wire to switch and a wire from the switch. Otherwise you have to have a junction box wired that way with a neutral, an unswitched and a switched wire from junction box to fan ceiling box. Just has to be.
    Found the box in the attic. It is black to red, white to white, 2 black capped, 2 white capped. "Cable" coming out of this box goes into the floor/ceiling of room underneath. In that 'cable' is a blue wire, black wire and white wire (as posted originally)

    I'd deduce that the blue wire coming from this box is the ground BUT the old fan had a blue wire coming from it that connected to this wire and we thought the blue wire worked the light kit for that fan.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #18

    May 26, 2009, 05:39 PM

    OK, I'm going to have to digest this for a minute.

    How did you determine that the blue wire was a ground? Is it connected to bare or green wires in the junction box.
    nojobtakesjust5's Avatar
    nojobtakesjust5 Posts: 10, Reputation: 1
    New Member
     
    #19

    May 26, 2009, 06:02 PM
    Quote Originally Posted by hkstroud View Post
    OK, I'm going to have to digest this for a minute.

    How did you determine that the blue wire was a ground? Is it connected to bare or green wires in the junction box.
    It was just a guess.

    Thing is the box in the attic has black-red-white-white wires (like wall switch) coming out of that box is a cable which feeds downward to go through the floor/ceiling to connect to the ceiling fan.

    Somehow a blue wire magically appears coming out of that 'cable' that comes out of the box in the attic. I say magically as until it comes out of that cable, you have not seen a blue wire. Not in the wall, not in the attic, etc. You also no longer see a red wire.

    Out of the cable or ceiling is blue, black, white and that's what we'd be connecting to the fan's striped, black, white.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #20

    May 26, 2009, 06:30 PM

    You tell me what to add, change or take away
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Ceiling Fan with no white wire in ceiling [ 2 Answers ]

Hello all, I'm trying to install a ceiling fan in an old house (about 60+ years). I have a new ceiling fan with 4 wires, black, blue, white, and green. On the ceiling, there are only three wires, 2 copper wires (unfortunately no colors, just a dark covering over both), and a green wire, which has...

Ceiling fan replacement [ 5 Answers ]

How much should I pay to have a ceiling fan replaced in the suburbs of Chicago?

Replacement globe for ceiling fan [ 1 Answers ]

I am looking for a Hampton Bay ceiling fan globe. It is a 10" mushroom white glass.

Wiring for ceiling fan replacement [ 10 Answers ]

I am replacing a ceiling fan. The old fan had black. Blue, white and green wires. This fan was wired black to black, blue to red, white to white, and green to green. The new fan has only black, white and green. It is remotely controlled. The electrical box on the ceiling has black, red,...

Bulb replacement for ceiling fan [ 4 Answers ]

I have a Hamption Bay "Lazerro" ceiling fan I just bought from Home Depot. I can not find a replacement bult. The bulb is a coiled 4 pin compact fluorescent with a slotted area on both sides in the middle of the bulb. The only ones that Home Depot carried as replacemets had the slotted area off set...


View more questions Search