    Need to rewire a series of lights
    I live in a very old house with a maze of wires running all over the place. I'm in the process of simplifying. I'll keep this as brief as possible. I want the power to run to the light, not the switch like all the diagrams I've come across say to do. So, from the breaker to the light, then from that box one line to run down to the switch and another line to run to the kitchen light. And can I do this with 2 conductor wire? (Not sure if that's the right terminology... I mean wire with a black, white and ground.)
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Apr 11, 2009, 11:26 AM
    You can legally and safely run a 2-wire switch loop from the light down to the switch, but then you will not have a neutral to continue power on to the kitchen light switch.
    So the answer is no, you cannot do it with only 2-wire cable.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Apr 12, 2009, 08:22 PM
    Stan
    Please note.
    (I would assume another line is another line from the light box to the kitchen light box)

    Quote Originally Posted by nyogha View Post
    breaker to the light, then from that box one line to run down to the switch and another line to run to the kitchen light.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Apr 12, 2009, 08:25 PM
    Maybe I did read it wrong. I took it that the kitchen light will be switched separately.

    If not then he would still need 3-wire between the first light and the switch.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #5

    Apr 12, 2009, 08:41 PM
    I think you are talking about an un-switched light. The light is on whenever the circuit breaker is on? Other than why on earth would you want to do this, I have a couple other questions, which I will make assumptions about.

    If so, you wire it just as you would a receptacle. You are using "two wire cable," so I assume you mean Type NM (AKA "Romex") This is a black wire, and a white wire, and a bare wire, covered by an overall plastic covering (jacket).
    The black wire is called the "hot" the white wire is technically called the "groundED" conductor, but most folks refer to it as the "Neutral. A bare or green wire is the "groundING" wire.

    I am also assuming you have only one circuit breaker panel in the house (there are no sub-panels, just the one connected to the electric service)

    At the light socket, connect the black wire to the brass screw, and the white wire to the silver screw, and the bare wire to the green screw. If you are using metal boxes, you also need to connect the grounding wire to the box.

    At the circuit breaker box (the Service Panel) connect the white wire and the bare wire to the Nuetral buss. (If you are wiring a sub-panel, these wires go to separate busses) and the black wire to the circuit breaker.

    Safety: Make sure the circuit breaker is OFF before connecting the wire. To be really safe, turn off the Main breraker. NOTE: Even with the Main breaker off, the wires coming from the electric company into the service panel are still live.

    If you are using a 20 amp breaker, all circuit wires need to be No. 12 AWG. If you are using a 15 amp breaker, you can install No. 14 AWG and save a few bucks.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    Apr 12, 2009, 09:48 PM

    Sorry Stan,
    Just reading the question as poster wants to know if 2-wire cable can be used to feed the fixtures, (with a switch leg) instead of feeding the switch as is shown in some do-it-you-self wiring diagram.
    Attached Images
     
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #7

    Apr 12, 2009, 09:51 PM

    I live in a very old house with a maze of wires running all over the place. I'm in the process of simplifying. I'll keep this as brief as possible. I want the power to run to the light, not the switch like all the diagrams I've come across say to do. So, from the breaker to the light, then from that box one line to run down to the switch and another line to run to the kitchen light. And can I do this with 2 conductor wire? (Not sure if that's the right terminology... I mean wire with a black, white and ground.)

    OK.. re-read the question! What I think you are saying is the "home run" from the service panel is the to the box with the light (Box A). From that box, you want to go to a switch (Box B), then to another light (Box C). The switch will control the light, and the circuit will continue in Box C.

    You will need a 3 conductor cable to run from box A to B, (Black, White, Red, and Ground) and a 2 conductor cable from box B to C. (Black, White, Ground)

    Note: The bare grounding wire is not included when you specify number of wires in a cable. You tell the supply house you want 12-2G or 14-3G cable, etc.

    At box A:
    1. Connect the white wires from the home run and the cable going to box B together, and "pigtail" them to the white screw on the light fixture.
    2. Connect the red wire to the brass screw on the fixture.
    3. Connect the two black wires together.

    At box B:

    1. Connect the black wires from box A and C together, and pigtail them to one screw on the switch.
    2. Connect the red wire to the other screw on the switch.
    3. Connect the white wires from box A and C together.

    At box C:

    You have one unswitched hot wire (Black) and one neutral wire. (white) You can continue the circuit from there.

    If you are not going to continue the circuit from box B:

    At box A:

    1. Connect the black wires from the home run and box B together.
    2. Connect the white wire from the home run to the silver screw on the light fixture.
    3. Mark the white wire from box B with a wrap of electrical tape, and connect it to the brass screw on the light fixture.

    At box B:

    Connect the white and black wires from Box A to the screws on the switch.

    As usual, connect the grounding wires to the green terminals on the devices, and also to any metal boxes.

    Hope this helps!
    nyogha's Avatar
    nyogha Posts: 3, Reputation: 1
    New Member
     
    #8

    Apr 12, 2009, 10:41 PM
    Quote Originally Posted by hkstroud View Post
    Sorry Stan,
    Just reading the question as poster wants to know if 2-wire cable can be used to feed the fixtures, (with a switch leg) instead of feeding the switch as is shown in some do-it-you-self wiring diagram.
    Is there anything wrong with this diagram? I'd like to use this solution if I can. I'd prefer to use 2 wire cable because I already dealt with the kitchen light/switch a couple of months ago.(I went to replace just the kitchen light fixture and found some melted wire nuts and other surprises) The 12-2G running from the laundry room light to the kitchen light doesn't need to be replaced, but I need to run new wire from the breaker to the laundry room light and to the switch.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    Apr 13, 2009, 05:28 AM
    Quote Originally Posted by nyogha View Post
    Is there anything wrong with this diagram?
    I assume that your question is for Stan, however I assure you that this is a perfectly legal, usual, and most often used method of wiring. Nothing wrong with the diagram (unless I made some dumb error drawing it.)
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #10

    Apr 13, 2009, 06:27 AM

    HK's drawing looks good, and most efficient.
    nyogha's Avatar
    nyogha Posts: 3, Reputation: 1
    New Member
     
    #11

    Apr 13, 2009, 07:19 AM
    Quote Originally Posted by hkstroud View Post
    I assume that your question is for Stan,
    Nope, it was for anyone who could provide a strong argument why your method would be wrong. Thanks for the help and thanks for everyone's input.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #12

    Apr 13, 2009, 09:47 AM
    Quote Originally Posted by Stratmando View Post
    HK's drawing looks good, and most efficient.

    Exactly. The lights will work as drawn. Just make sure to mark the white "switch legs" with a wrap of electrical tape so not to confuse them with neutrals.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

German shepard dog television series just want to know the name of the series! [ 4 Answers ]

Does anybody know of a dog series that was on TV during the early 90s. Where its main focus was a german shepard, who would help people in all the different episodes. I Remember the song of the TV series which went like this " until tomorrow I am going to settle down" Its not lassis just would...

How to rewire a chandlier [ 2 Answers ]

I am trying to rewire a chandlier, what wires go where?

Rewire bath lights and fan [ 1 Answers ]

In existing bathroom, we have one switch that turns on the vanity light and the bathroom exhaust fan and a second switch that turns on a heat lamp. I would like to rewire so that the heat lamp switch would also turn on the exhaust fan. The simplest would be if I could run wires from the heat...

Rewire kitchen.. [ 1 Answers ]

Sorry forgot to ask in my earlier post. When I re-wire my, kitchen, (size about 10x10, Florida block house) this is what I have planned. Run my stove line. run 2: 12-2 homeruns for counter outlets. 12-2 for dishwasher 14-2 shared for fridge and garbage disposal. (can I do this?) 12-2...


View more questions Search