    Replacing a GFCI Receptacle
    I have a bad GFCI outlet in my garage. How do I determine whether it is a 15amp or 20amp outlet. The bad outlet does not have a label that states the amps. The circuit breaker is 15. Does this mean I use a 15amp? Can I use a 20amp to replace it?
    ZoeMarie's Avatar
    ZoeMarie Posts: 2,049, Reputation: 468
    Ultra Member
     
    #2

    Nov 30, 2008, 01:17 PM

    You would want to stay with a 15 amp outlet. If you want to change the whole circuit to 20 amps you could but that would be a lot more work than replacing the outlet you have with another 15 amp outlet.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Nov 30, 2008, 04:10 PM
    Most "standard" receptacles in a home are 15A. Unless you are in Canada there is NO reason to use 20A receptacles, even on a 20A circuit, unless a certain appliance or tool requires it.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Dec 1, 2008, 08:49 AM

    Opinion.

    I prefer to use a receptacle that matches the circuit.

    I like to know that the receptacle matches the breaker and conductors.
    ZoeMarie's Avatar
    ZoeMarie Posts: 2,049, Reputation: 468
    Ultra Member
     
    #5

    Dec 1, 2008, 09:29 AM
    Quote Originally Posted by donf View Post
    Personal opinion.

    I prefer to use a receptacle that matches the circuit.

    I like to know that the receptacle matches the breaker and conductors.
    I had to spread the rep. but being consistent is the safest way to go!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Dec 1, 2008, 09:58 AM
    Quote Originally Posted by donf View Post
    Personal opinion.

    I prefer to use a receptacle that matches the circuit.

    I like to know that the receptacle matches the breaker and conductors.
    This is not really a valid point as ALL 15A receptacles are 20A feed-through.
    The slots in the front are the ONLY difference.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Dec 1, 2008, 03:46 PM
    Stan,

    The slots in the front are identifiers for the circuit behind it.

    If you are looking at a standard 15 Amp receptacle, you expect a 15 Amp breaker upstream at the panel and therefore you know that the breaker is limited to a 12 amp load for the entire circuit.

    If you are looking at a 20 receptacle, then your expectation is that there is a 20 amp breaker, 12 AWG conductors and you are limited to 16 amps for the total circuit.

    Again it's just my opinion not dogma at all.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Dec 1, 2008, 04:25 PM
    I understand this is only your opinion, I am just trying to give you some clarification.



    Quote Originally Posted by donf View Post
    The slots in the front are identifiers for the circuit behind it.

    If you are looking at a standard 15 Amp receptacle, you expect a 15 Amp breaker upstream at the panel and therefore you know that the breaker is limited to a 12 amp load for the entire circuit.
    In the US this is absolutely NOT true. A 15A duplex can have either a 15 OR 20A circuit feeding it. In some homes all the general use receptacles are fed by 20A circuits.

    With regard to 15 & 20 amp circuits the receptacle face is not nearly always an indication of circuit size.

    You can certainly do it any way you like, but in most homes this is the case.





    Quote Originally Posted by donf View Post
    If you are looking at a 20 receptacle, then your expectation is that there is a 20 amp breaker, 12 AWG conductors and you are limited to 16 amps for the total circuit.
    A 15A-240v circuit with a simplex receptacle will likely have a 15/20A rated receptacle. 210.21(B)(1)

    Also, a 20A circuit is NOT "limited" to 16 amps. It is limited to 16 amps continuous. There is not much, other than lighting, that would be considered a continuous load in a residence.
    Remember, a continuous load is something that is expected to remain on for 3 hours or more. Something being left on by accident does NOT constitute a continuous load.

    A receptacle is limited to a certain load See the wording in 210.21(B)(2)
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #9

    Dec 2, 2008, 11:50 AM

    The answer to the original post is that you MUST use a 15A receptacle if you have a 15A circuit, which you do.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Dec 2, 2008, 04:41 PM
    The first question:

    Quote Originally Posted by hokiehawk79 View Post
    How do I determine whether it is a 15amp or 20amp outlet.
    Has not been answered.

    I attached photos of a 15 amp and a 20 amp receptacle.

    The one on the left with a Tee slot is the 20 amp.

    The other with both blades parallel is the 15 amp, and the only one you should find since you have a 15 amp circuit breaker.

    Do not use a 20 amp receptacle on a 15 amp circuit.
    Attached Images
      

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Receptacle GFCI [ 3 Answers ]

I have a GFCI Receptacle is my main bathroom that is not working at all it has 1 black wire 1 white wire and a ground, I have the same outlet in my other bathroom and it works fine it has 2 black wires 1 white wire and a ground, I was wondering if the lack of a black wire is my problem or can it be...

Gfci receptacle [ 3 Answers ]

I Would Like To Know If You Can Install A Gfci Recep. On A Shared Neutral Circuit.

GFCI Breaker vs Receptacle [ 1 Answers ]

I'm adding some 20A circuits in my garage/shop and know that they have to be GFCI protected. My question is this: Is there an advantage to using a GFCI breaker over just putting a GFCI receptacle in the first slot of the series? Thanks.

GFCI Receptacle [ 1 Answers ]

Do they make a slimline GFCI Receptacle? I have some very narrow metal eletrical boxes in my kitchen and the regular size GFI will not fit.

Installing a gfci receptacle [ 3 Answers ]

I am trying to install a gfci receptacle in my offfice( replacing the existing regular receptacle) I have two black wires that were wrapped together , two gray wrapped together, one single blue and one green. I followed the directions and think I got all the wires to the right place. The test light...