    I want to wire a shed that is 225 ft from power I want 40 amps of service what size wire do I need for 220 volt?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Apr 1, 2008, 04:02 AM
    I'd use #4 and a 50 or 60A breaker, not 40A.
    You need to upsize the wire for that distance. This is NOT a code requirement, it is a code recommendation.


    Using #6 you can pull up to 40A breaker up to around 180'.
    If you jump to #4 you can pull almost 60A at 225'. Even at a full 60A the VD is NOT severe enough to even worry about.
    So use the #4, but don't limit yourself at the same time. Take advantage of the larger wire.

    What will you be using out there?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire Size and panel size [ 6 Answers ]

I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...

Wire size etc [ 3 Answers ]

The other day, I read where a supposedly Electrician, could not find the size wire he needed, i.e., # 2 Copper, for, from meter to Fuse panel.. and, this guy told the owner, he could put one or two, of a smaller size, tie them togather to create a larger size wire to carry the heavier load.. the...

Wire size etc. [ 1 Answers ]

Back to Honduras, where the NEC don't apply.. I am installing a 150 amp service.. and it is about 100 ft from breaker panel to meter, and about 50 ft from meter to utility pole connection.. These people commonly use aluminum, and # 2 awg is the largest I can find.. Does anyone think this is...

Wire size [ 1 Answers ]

What size wire should I use from the electrical meter to feed a 200 amp service panel in a 40' x 60" garage/barn? The run is about 10 feet long.

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search