    Wire size etc.
    Back to Honduras, where the NEC don't apply.. I am installing a 150 amp service.. and it is about 100 ft from breaker panel to meter, and about 50 ft from meter to utility pole connection..

    These people commonly use aluminum, and # 2 awg is the largest I can find.. Does anyone think this is adequate, for a 150 amp service?

    I have been told, by people here, that aluminum, #2 is OK from the meter to pole, but if I use the same wire from breaker to meter, the aluminum will heat up and cause excessive reading and thus more charges through the meter.. and that I should use copper from breakers to meter to prevent this, make sense? thanks for any input..
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 28, 2007, 12:36 PM
    Insulated #2 on a messenger in free air is good for 123 amps. Most utilities use #2 for 150 amps, and #1 for 200 amp services here. What is the likelihood that your draw would be actually 120 amps?

    But once in conduit, your aware that wire will heat up more quick since the heat cannot dissipate, so copper would be a good plan.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size [ 2 Answers ]

I am wiring a barn/shop fed by a 100 amp service. Some of the outlets may be over 70 feet from the panel (all will be 20 amp breakers). Should the wire size I pull in for these outlets be 10awg rather than the normal 12awg? My question relates to voltage drop. The shop is about 50'x 70'. Two big...

Wire size [ 1 Answers ]

What size wire should I use from the electrical meter to feed a 200 amp service panel in a 40' x 60" garage/barn? The run is about 10 feet long.

Wire size [ 3 Answers ]

What size wire should you use for a 125 amp three phase circuit? How do you figure that for future reference?

What size wire to use for new service? [ 2 Answers ]

We are currently building a greenhouse, and I need to run about 240 foot of wire from the pole to the greenhouse breaker box. The greenhouse will have 2- 115/230V fans drawing 6.0 amps each, 3- 1/3hp sump pumps not sure of the amperage yet but will be 115v, LP gas instant hot water heater, 10...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search