Ask Experts Questions for FREE Help !
Ask
    MayMay22's Avatar
    MayMay22 Posts: 5, Reputation: 1
    New Member
     
    #1

    Mar 5, 2008, 09:49 AM
    240 Volt oulet with dead white wire
    I recently moved into a 2 year old house. My electric clothes dryer was only getting partial heat and we traced the problem to the 240volt electrical outlet. We tested the wires at the panel and both breakers gave a reading of 122 volts. After we could not get the right reading on the actual outlet, we removed it and tested the wiring alone. We get no reading from the white wire. There happened to be a third (red) wire capped in the outlet box, that when we tested it, was good for 120volts. We used this red wire to connect the outlet with. My question is: Is is safe for me to leave that white wire capped in the outlet, or should I have an electrician come and try to pull it out since we did get a live reading for that wire in the panel.
    I don't want to burn down my new house.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Mar 5, 2008, 10:10 AM
    What type of cord do you have on the dryer? 3-wire or 4-wire. If you have a 4-wire cord, you will require a 4-wire receptacle and will have a connection place for the white wire. If you have a 3-wire cord and the receptacle is for 3-wire (which I suspect) you are fine capping the white wire.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Mar 5, 2008, 11:07 AM
    To add to strouds' input. If it is 3 wires, you need to have 240 volts between the 2 hots,
    Then connect the ground to center of receptacle.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Mar 5, 2008, 02:20 PM
    NO, you are NOT fine capping the white wire. Also, you do NOT install the receptacle to match the cord, your install a cord to match the receptacle.

    I am not sure how it was connected before, but if one of the INSULATED wires was capped off it was wrong.

    You MUST use three INSULATED wires to connect to the receptacle if NM cable was used (which is the case since you say there is b, w & r).

    If you have a 3-prong receptacle (which I suspect) you use the black, red and white wires to it. The black and red are your two hots and the white is the NEUTRAL.

    If the existing receptacle is a 4-prong then you must also use the ground.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Mar 5, 2008, 02:24 PM
    An electric dryer is a 120/240v appliance. NOT a 240v appliance. They also follow the same rules as 120/240v household kitchen cooking appliances.

    Please see this thread for plenty of information on this topic:
    https://www.askmehelpdesk.com/electr...nd-185686.html
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Mar 6, 2008, 06:43 AM
    Just noted 2 year old house, New construction and remodel require 4 wire, it should have had 4 wire receptacle and a 4 wire cord installed on dryer. Looks like someone had a 3 wire dryer and felt it easier to change receptacle than cord.
    MayMay22's Avatar
    MayMay22 Posts: 5, Reputation: 1
    New Member
     
    #7

    Mar 6, 2008, 08:26 AM
    Quote Originally Posted by Stratmando
    Just noted 2 year old house, New construction and remodel require 4 wire, it should of had 4 wire recepticle and a 4 wire cord installed on dryer. Looks like someone had a 3 wire dryer and felt it easier to change recepticle than cord.
    I agree that someone installed the wrong plug and therefore didn't need all the wires.
    To fix the problem, should I intall a 4 wire plug? If so, will it still work knowing there is no voltage reading on the white neutral wire?
    At the panel, the black and red wires are going to the breakers. The white wire is going to a neutral. We did not get any reading on our voltage meter when we touched the white wire. I DO have a 3 wire plug in, to which we hooked up 2 hots, (red and black) and the ground in the middle. I have the white capped.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Mar 6, 2008, 01:52 PM
    Yes, you ABSOLUTELY should replace the receptacle AND cord with 4-wire units.

    The hook ups are the same only you are using both the white and ground.
    You should get not a voltage reading from white to ground.
    You should get a voltage reading from hot to white.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #9

    Mar 6, 2008, 03:54 PM
    When You install the Receptacle, Hots to the outside, Ground will have strap connecting to receptacle metal body, and green to ground.
    Xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx
    When you install the cord, Hots to the outside on dryer, The center is a little tricky. Remove the strap that connects the center of the 3 terminal studs(On dryer). This is now Your Ground and Neutral Separated. The White goes to center terminal, and the Green goes where the strap was(The metal body of the Dryer). Don't use strap. Turn Power off.
    Like stanforty says, no voltage on Neutral as they are both connected together at your electrical Service.
    The difference is the Neutral carries current, and the ground carries current when a fault occurs.
    A drill may use a black(hot and neutral)white for power, and the case of the drill grounded. If you drilled into a Live wire it will touch ground, trip breaker, and not become Live?Dangerous).
    When you have a 3 wire(Range or Dryer)the 3rd wire(Ground is carrying current)Ground is NOT to Carry current.
    This would have current flowing through. A potential for voltage.
    It probably took 100 Years for someone to make it happen, I thought about it myself, and was an NFPA member, and accepted it. I never Back wire recepticles even though code allowed years ago.
    Take Care
    biggsie's Avatar
    biggsie Posts: 1,267, Reputation: 125
    Ultra Member
     
    #10

    Mar 6, 2008, 05:48 PM
    This picture is for dryer -- 3 prong and 4 prong diagram

    Appliantology Archive: Dryer Cords

    Red wire and black wire are hot they are LINE on the diagram ( L1 & L2 )

    The WHITE wire is the Neutral wire -- Marked ( N ) same on 3 or 4 prong plug

    The GREEN is the GROUND on a 4 Prong Plug -- connects to the case or chassis

    In the breaker panel a 220 volt breaker is required -- RED & Black Wire lug in

    The WHITE wire Lugs where all the other WHITE wires lug

    Green lands on GROUND -- and should run from panel to ground stake

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

240 volt to 120 v [ 3 Answers ]

I'm looking at buying a few tools from america, which I understand run on 240 volts. I want to know if its possible to change it to 120volt by just changing the lead. Cheers:D

240 volt wiring [ 1 Answers ]

When wiring my weldershould I use neut bus or grnd bus to grnd the machine

2 wire 240 connect to 3 wire 120/240 [ 2 Answers ]

I am in the process of hooking up a new Electric Range. It has a three wire connector terminal block ). My existing wiring is 1970's vintage alum, but inspected and in good condition. The existing wire in 8 gauge two wire (black and white) plus ground. Do I have to run a new wire all the...

240 volt four wire in 240 three wire outlet [ 1 Answers ]

I have a generator that has (2) 20 amp 110 outlets and (1) 240 outlet. The 240 outlet have receptacle for four wire plug but I want to use it in a three 930 wire 240 volt plug at other end. Is this a workable solution?

Replacing a 240 volt outlet with a 120 volt oulet [ 1 Answers ]

We've switched to a central air conditioning system and no longer need the 240 volt outlet by the dining room window. The house was built in 1928, updated in 1957, and again a couple of ad hoc times thereafter. The wiring is at times very old, brand new or somewhat old. My guess is that the 240...


View more questions Search