    Max number/size breakers.
    I have a Square D 100A main. There is no main breaker in the panel. What is the most number/size of breakers I can put in it. Right now I have 10 Slots. A 30amp, 5 20 amps and 4 15 amps. If I change the breakers to tandem breakers what is the max amps I can put in? Right now I have 190 amps. If I swap out to tandem I can go to 350 but I don't know what the formula is for determining the max?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 4, 2008, 05:03 PM
    No more than 42 circuits can be in any one panel, The load does not go by the count or total amps of the branch circuits. The load connected to the panel can be calculated depending on the type of circuits that will be in the panel, such as a home, addition, shop, store.

    If this is a home, need total square footage of livable space, list any major electric appliances type of heat and size AC to size a service or panel.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Feb 4, 2008, 07:05 PM
    You say you want to go from 190 to 350 Amps, that sounds like a 60 and a 100 amp breaker?
    rgman's Avatar
    rgman Posts: 7, Reputation: 2
    New Member
     
    #4

    Feb 5, 2008, 08:26 AM
    Quote Originally Posted by tkrussell
    No more than 42 circuits can be in any one panel, The load does not go by the count or total amps of the branch circuits. The load connected to the panel can be calculated depending on the type of circuits that will be in the panel, such as a home, addition, shop, store.

    If this is a home, need total square footage of livable space, list any major electric appliances type of heat and size AC to size a service or panel.

    Sq Footage is 1224. Electric Range, and Fridge are the only two big items.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Feb 5, 2008, 08:31 AM
    Is this panel for a full home? Including washer, dryer (gas I assume) hot water, heat, air conditioning?

    Please explain the reason for your question on size of panel.
    rgman's Avatar
    rgman Posts: 7, Reputation: 2
    New Member
     
    #6

    Feb 5, 2008, 08:34 AM
    Quote Originally Posted by tkrussell
    Is this panel for a full home? Including washer, dryer (gas I assume) hot water, heat, air conditioning?

    Please explain the reason for your question on size of panel.
    It is for a full home. Washer and dryer is on a dedicated 15 amp. (dryer is gas), Hotwater is gas. I am looking to expand the panel because I want to put in Central air and heat. Currently there is no central air or heat only wall furnaces.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Feb 5, 2008, 08:37 AM
    What kind of heat and size AC are you planning? I need those sizes to do a complete service rating. I am assuming you want to know the total calculated load that will be connected once the renovations are completed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

If I register for a business number in Canada and provide my social Insurance number. [ 1 Answers ]

If I register for a business number in Canada and provide my social Insurance number.. ... will my SIN always be "connected" with my business? In other words, as far as Canada REvenue is concerned are they 2 different entities? I want to apply for Bus # for a sole propriatorship

Breaker Box Amps rating & Number of breakers installed [ 1 Answers ]

I have a question in regards to amps allowed in a breaker box. My breaker box has a label stating that the box has a maximum load of 200 amps, but that it is convertible. I really don't know what the convertible part means. If I look at the breakers installed, these add way more than 200 amps. ...

Max pipe size in load bearing walls [ 2 Answers ]

I have a 2" line stubbed for a drain in an area of a 15' basement that will be framed 8' high with the rest used for storage above. Are these walls now considered load bearing? What's the maximum size pipe I can run through a load bearing 2x4 wall assuming I'm using a protective plate.

Size of Copper/pvc inside new home to max pressure from 3,000 gl tank on hill [ 1 Answers ]

Hi, I am building a new home in the country and have a 3000 gallon water tank 75 verticle above my (future) second story. I was going to have either 2" sch 40 pvc or 1 1/4" come down the 160 feet to my home. And then I wanted to know what is the largest copper pipe I could use inside the home to...


View more questions Search