    Bryant furnace won't run looking for guidance to check
    I have a Bryant Furnace Model 383KAV042091
    At the beginning of the summer the air conditioning would not come on so I installed a knew thermostat. It came right on. Now as winter approaches we switched to Heat and the furnace will not come on.
    The air conditioner works, when I flip the switch to cool , the fan motor runs when I flip to "Fan" at the thermostat.

    I did a test on the board test tab to com 24 (while having red wire from thermostat disconnected.
    LED light blinks 1 short 1 long 4 times then the inducer motor comes on, seems to run fine, igniter glows, fan kicks on, lower speed then to higher speed, test is over.

    When I have the thermostat calling for heat inducer motor does not start up. I can not check the voltage at the pressure switch which I believe is suppose to be 24v DC.
    Just looking for method of attack, not sure which comes first the chicken or the egg.
    Thermostat calls for heat, should the inducer motor start before the pressure switch, before the igniter I thought maybe it was a stuck inducer motor relay if in fact that is what is suppose to start up first. The best I can tell the relay is on the PCB.. I really hope I do not need to replace the PCB looks like over $250.. but you got to do what you got to do. It gets rather cold in Northern Indiana
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Oct 15, 2007, 09:08 AM
    Go to the sticky at https://www.askmehelpdesk.com/heatin...ons-58313.html
    And work your way through the sequence of operations.
    Nooner's Avatar
    Nooner Posts: 1, Reputation: 1
    New Member
     
    #3

    Oct 20, 2009, 07:09 PM
    Did you remove the jumper wire on the t-stat between rc and rh? There should be one there.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant furnace problem [ 20 Answers ]

Hi All, I have a 5 y/o 80% eff bryant furnace. The problem I have is that my furnace Doesn't always kick on even when thew thermostat shows the temp under the Temp set. I will sometimes have to go down and turn of the blower switch on the furnace wait a couple seconds and then turn it on again....

How to run fan only to circulate the air Bryant 395CAV [ 1 Answers ]

Hi, I am new to this forum and beginner in heating system. I would like to know if there is a way to rewired or jumped wires to make the fan run only (without heat) to circulate the air fom the basement. My furnace is a Bryant model 395 CAV Series G, thermostat is only 2 wires. If I have not...

Bryant Furnace Burner Going On and Off [ 1 Answers ]

Bryant Gas Furnace P/N 394DAC03100 about 30 yrs old. Pilot light stays light and burner going on and off after checking valve problem seems to be some type limit switch when I move the wiring by shaking a little it ignites. Having a problem finding which wires are loosely connected..? If anyone...

Bryant furnace won't lite [ 3 Answers ]

Hello, I have a Bryant furnace. It Keeps flashing code 13 on the circuit board. I read the code and it says that the switch will reset after 3 hours. It also refers me to # 33 which gives more possibilities as to what the problem may be. However it does say to reset the limit or flame roll out...

New Bryant A/C compessor will not run [ 1 Answers ]

I have a newly installed Bryant 2 1/2 ton compressor unit that was installed in August 2005. When I turned on the A/C the unit would not start. I checked the disconnect near the compressor and found it to be faulty and replaced it with a new one and there is still no start up. I pulled the panel to...


View more questions Search