New Member
|
|
Apr 15, 2016, 06:28 AM
|
|
Voltage drop and wire size
I need to install a 480v 3 phase panel 350' from the power source. I plan on running 2" emt to a main disconnect at the other end and setting a 480v delta to a 208 wye transformer and then setting a sub panel for 208/120v power. My calculations give me 3/0 cu or 4/0 al with a1.81% vd. Can you verify my calculations?
|
|
 |
Printers & Electronics Expert
|
|
Apr 15, 2016, 07:02 AM
|
|
Just to level set you, this is a DIY, residential site, not a commercial building site.
That said, we need to know the amperage that you are going to deliver to the main disconnect switch, please.
Also, I'm just curious, why are you putting the main disconnect in front of the transformer rather than at the secondary feed into the service panel?
|
|
 |
New Member
|
|
Apr 18, 2016, 05:30 AM
|
|
 Originally Posted by donf
Just to level set you, this is a DIY, residential site, not a commercial building site.
That said, we need to know the amperage that you are going to deliver to the main disconnect switch, please.
Also, I'm just curious, why are you putting the main disconnect in front of the transformer rather than at the secondary feed into the service panel?
The main disc. Switch is a 225 amp feeding a 75kva transformer. I need a disconnect in front of the transformer because it is so far away from the power source. I would need a means to kill it close to the panel
|
|
 |
Printers & Electronics Expert
|
|
Apr 18, 2016, 07:24 AM
|
|
Okay, but normally you would fuse protect the primary/secondary of the transformer and then feed the disconnect switch.
Just curious, but is the disconnect switch's purpose to shut down the transformer when the site is not being used, as in a vacation home?
My calculator (480v/200 amp - 2% voltage drop) comes up with 4/0 copper conductors type THWN-2. I would suggest using schedule 80 PVC because underground is a wet location. EMT may rust out on you.
The same reason (wet location) I would use a an insulation type that is listed for wet locations.
Using copper for the 350' run will be expensive!!
|
|
 |
New Member
|
|
Apr 19, 2016, 05:09 AM
|
|
 Originally Posted by donf
Okay, but normally you would fuse protect the primary/secondary of the transformer and then feed the disconnect switch.
Just curious, but is the disconnect switch's purpose to shut down the transformer when the site is not being used, as in a vacation home?
My calculator (480v/200 amp - 2% voltage drop) comes up with 4/0 copper conductors type THWN-2. I would suggest using schedule 80 PVC because underground is a wet location. EMT may rust out on you.
The same reason (wet location) I would use a an insulation type that is listed for wet locations.
Using copper for the 350' run will be expensive!!
Thank You. I came up with the same wire size. I wasn't sure if I did the calculation correctly so you have answered my question.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Cable size, voltage drop, 3phase
[ 5 Answers ]
Hi
I asked to move 3 phase transformer to new pole.
This 3 phase transformer is feeding apartment building from pole to underground service.
Currently this tx 3-50kva ,600/347 V, 4-4/0 Al.
they gave me the peak load on tx is 135 kva.
77 residents in apartment all 120/240. But I don't know...
Voltage drop