Ask Experts Questions for FREE Help !
Ask
    met66's Avatar
    met66 Posts: 2, Reputation: 1
    New Member
     
    #1

    Jun 28, 2012, 07:01 AM
    Voltage drop
    Up until 2 weeks ago my spot lights were working fine, switched on 1 day and they popped checked voltage at light point and it was 70v. Disconnected switch line at switch checked voltage on feed and it was OK at 235v .Whilst still disconnected from switch I send a live feed up switch line and got 235v at lighting point OK. Disconnected lights, reconnected switch line to switch checked voltage at lighting point and it dropped to 209v ,reconnected lights 1 by 1 (with a 12v transformer) and there was a voltage drop each time( there is 3 way switching for lights) can someone advise me ?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 28, 2012, 07:05 AM
    Having a difficult time trying to follow the circuit.

    Can you list the devices in order from panel to switch to light, etc.

    What is 235 volts?

    Does the 235 volt feed go to lighting transformers?

    Is this all underground wiring?
    met66's Avatar
    met66 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 28, 2012, 12:47 PM
    Quote Originally Posted by tkrussell View Post
    Having a difficult time trying to follow the circuit.

    Can you list the devices in order from panel to switch to light, etc.

    What is 235 volts?

    Does the 235 volt feed go to lighting transformers?

    Is this all underground wiring?
    Hi from what I can see the feed comes from the panel to a terminal junction box which then splits and feeds other lighting circuits. One feed cable goes to another junction box which is where the spot lights are wired to, from this box a cable goes down to feed the switch and a return wire as the switch line, The power going to the switch is OK it's when it comes back on the switch line the voltage is lost. There are 3 switches as there are 3 points to switch the lights from. The 235v go to 12v transformers then lights. I have tested the switch line and there is no fault, could it be one of the switches?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jun 28, 2012, 02:27 PM
    Where are you located?
    You may have a burnt or coroded buss where the breaker plugs onto, a loose wire or connection, If you keep applying a little more load each time and the voltage drops that much.
    Are you sure the transformers Primary is 240(235) Volts?
    And if you have 3 switches, you will need 2 to be 3 ways, and 1 4 way.
    Are you using a low voltage dimmer with a relay box?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage drop [ 8 Answers ]

How do you compute voltage drop when given a specified distance and cable size?

Voltage drop [ 4 Answers ]

Can someone please post the formula for voltage drop? Many thanks.

Voltage drop [ 5 Answers ]

I will be running wire to my shop that is aprox 250' from the main elect box at the house. I would like to have 220 volts and 110 volts. The wire will be buried underground the average temp in my area in the summer is 100 degrees. What size wire should I use. I will be welding with a welder that...

Voltage drop [ 4 Answers ]

A 300sq mm cable is to be laid for 600mtr. Distance. As the distance is large so there are considerable voltage drop at the receiving side. How can we cope up with this voltage drop at the receiving end? We want a constant voltage ofd 415 V at receiving end irrespective of input voltage? ...

Voltage Drop [ 2 Answers ]

I have a 20 amp breaker;there are a total of 7 receptacles on this circuit with a 15 amp GFI on the first receptacle. The first 5 receptacles in line work fine, the last two receptacles which are approximately 70 feet from the 5th receptacle flip the 15 amp GFI off when plugging in a drill. I...


View more questions Search