Not your question?
Ask your question
View similar questions
Add your answer here.Check out some similar questions!
Do we need another transformer for 500 foot run and what gauge wire?
[ 5 Answers ]
We are adding a shed and will be running a new line from the electrical pole. The shed will be approximately 500 feet from the pole. Prior to the pole, this will also branch off to go to a new above ground pool to power the pump. Our question is if we can just run the line straight to the panel...
8 gauge wire with 20 amp breaker
[ 2 Answers ]
I have an A/C unit that was connected to the breaker box with 8 gauge wire and a 40 amp 240 volt breaker. The A/C unit is small and rated at 20 amps. Is there any significant risk in just replacing the 40 amp breaker with a 20 amp and not changing the wiring (would require breaking through...
What gauge wire do you use for a 20 amp breaker
[ 3 Answers ]
What gauge wire do I use for a 20 amp breaker
12 gauge wire to a 15 amp breaker
[ 6 Answers ]
I am selling my home and the inspector noted three 15 amp breakers with 12 ga wire. He flagged it as something to be checked by an electrician. Is this an unsafe situation? The buyer is concerned. How much of a concern should this be? If it is not unsafe, what is the explanation for why is...
What gauge of wire do you need to run off a 20-amp breaker?
[ 2 Answers ]
What gauge of wire do you need to run off a 20-amp breaker? View more questions Search
|