    8 gauge wire with 20 amp breaker
    I have an A/C unit that was connected to the breaker box with 8 gauge wire and a 40 amp 240 volt breaker. The A/C unit is small and rated at 20 amps. Is there any significant risk in just replacing the 40 amp breaker with a 20 amp and not changing the wiring (would require breaking through drywall,etc.)?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 17, 2012, 05:02 PM
    No, but why bother?

    When you say rated, what do you mean?

    A/C units have a minimum circuit ampacity and a max fuse/breaker size.
    What is the max breaker rating on your unit?
    baron4's Avatar
    baron4 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 17, 2012, 05:57 PM
    The minimum circuit ampacity is 13.0.
    The max breaker rating is 20.0.

    Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

8 gauge wire for 50 amp circuit breaker? [ 3 Answers ]

I have 50 amp circuit breaker for double wall oven. Wire from floor is al shielded so I bought 6-3 al shielded but when connecting at junction box, the floor wire is thinner than 6 gauge (8?). The oven also has thinner wire so can I splice in 6 gauge or should I use same gauge as existing from...

What gauge wire do you use for a 20 amp breaker [ 3 Answers ]

What gauge wire do I use for a 20 amp breaker

15 amp circuit breaker on 10 gauge wire [ 6 Answers ]

I want to run an outside light and receptacle about 250 feet from the main panel load center. It I use a 15 amp circuit breaker, is 10 gauge wire large enough?

12 gauge wire to a 15 amp breaker [ 6 Answers ]

I am selling my home and the inspector noted three 15 amp breakers with 12 ga wire. He flagged it as something to be checked by an electrician. Is this an unsafe situation? The buyer is concerned. How much of a concern should this be? If it is not unsafe, what is the explanation for why is...

What gauge of wire do you need to run off a 20-amp breaker? [ 2 Answers ]

What gauge of wire do you need to run off a 20-amp breaker?


View more questions Search