    Adding a 200 amp sub panel.
    My 200 amp Square D 40 breaker panel is full. Can I add a second 200 amp Square D panel that I already have as a sub?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 14, 2013, 07:13 PM
    No. The branch circuit breaker limitation is most likely 100 or 125A.
    You can feed the 200A panel with a 125A breaker but I advise against it. A 40 space panel as a sub might be too tempting to over load.
    acsconsulting's Avatar
    acsconsulting Posts: 6, Reputation: 1
    New Member
     
    #3

    Nov 15, 2013, 12:17 PM
    If I understand, there are two ways to handle this.

    Add a sub feed lug kit to the main panel and run wire to a main lug panel (sub panel 125a as you recommended? Or

    Pull two breakers from the main panel and replace them with a double power transfer breaker then run wire from the breaker to the sub panel.

    Am I correct, off base or need to add something?

    I should add that I have already doubled up on two breakers in the main panel and need the sub to eliminate that and add an outdoor fan and outlets to a gazebo. I'm sure more add ons are in the future.

    Thanks for your help Stanfortyman.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Nov 15, 2013, 03:12 PM
    Have you condidered having a "calculated load" completed to see if your residence is adequatley serviced. You may want to up your service to 300 amp and use a dual meter to feed both the residence's main service and the secondary panelboard.
    acsconsulting's Avatar
    acsconsulting Posts: 6, Reputation: 1
    New Member
     
    #5

    Nov 15, 2013, 05:55 PM
    Quote Originally Posted by donf View Post
    Have you condidered having a "calculated load" completed to see if your residence is adequatley serviced. You may want to up your service to 300 amp and use a dual meter to feed both the residence's main service and the secondary panelboard.
    My average daily usage is 38kwh or about 4 per hour.

    200amp service should be adequate for that. Correct?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Nov 16, 2013, 07:56 AM
    Have you condidered having a "calculated load" completed to see if your residence is adequatley serviced. You may want to up your service to 300 amp and use a dual meter to feed both the residence's main service and the secondary panelboard.
    Are you really suggesting a second meter to feed a sub-panel inside a residence?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Nov 16, 2013, 08:02 AM
    My average daily usage is 38kwh or about 4 per hour.

    200amp service should be adequate for that. Correct?
    That is not a load calculation, and really is not an indication of demand load.
    A real load calculation would be required.

    Unless the home is really big, like 3500 sq/ft+, and/or uses electric heat or a whole house on demand water heater, a 200A service should be more than adequate.
    Just adding a sub-panel does not add load. It's what you put in it that does.
    Why do you need another 200A panel? Just because you have it on hand?

    Personally I would not add a sub-feed lug kit to add a 200A panel to a 200A main panel. If you really need that much space then you actually may fit the description above requiring a 320/400A service.
    acsconsulting's Avatar
    acsconsulting Posts: 6, Reputation: 1
    New Member
     
    #8

    Nov 16, 2013, 10:46 AM
    Thanks. I realize that a load calculation is the way to go. I was just trying to show that the demand is not that heavy.
    The home is about 2500 sq. ft. with oil heat. 4 beds 3 baths. The larger draws would come from the furnace/ac, through wall heat/ac unit in garage, well pump, normal 220 appliances and 220 shop tools. All the 110 is standard for this size house.
    There is also a 45kw whole house automatic backup generator tied to the system.


    Quote Originally Posted by stanfortyman View Post
    That is not a load calculation, and really is not an indication of demand load.
    A real load calculation would be required.

    Unless the home is really big, like 3500 sq/ft+, and/or uses electric heat or a whole house on demand water heater, a 200A service should be more than adequate.
    Just adding a sub-panel does not add load. It's what you put in it that does.
    Why do you need another 200A panel? Just because you have it on hand?

    Personally I would not add a sub-feed lug kit to add a 200A panel to a 200A main panel. If you really need that much space then you actually may fit the description above requiring a 320/400A service.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    Nov 16, 2013, 11:57 AM
    I should add that I have already doubled up on two breakers in the main panel
    What does that mean?
    acsconsulting's Avatar
    acsconsulting Posts: 6, Reputation: 1
    New Member
     
    #10

    Nov 16, 2013, 04:39 PM
    Quote Originally Posted by hkstroud View Post
    What does that mean?
    Two circuits run off one breaker.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #11

    Nov 16, 2013, 06:17 PM
    Sound to me like all you need to do is replace 4 regular breakers with 4 twin or slim line or piggy back breakers. That would allow you correct the doubled up breakers and give you two additional breakers for the circuits you need.
    acsconsulting's Avatar
    acsconsulting Posts: 6, Reputation: 1
    New Member
     
    #12

    Nov 16, 2013, 06:58 PM
    Quote Originally Posted by hkstroud View Post
    Sound to me like all you need to do is replace 4 regular breakers with 4 twin or slim line or piggy back breakers. That would allow you correct the doubled up breakers and give you two additional breakers for the circuits you need.
    Thanks Harold. That will work for now. I will worry about future expansion when the need arises.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp. Main panel, fed from the meter. How do a I Install a 200 amp sub-panel [ 3 Answers ]

I have a 200 amp panel, fed from the meter located in the house. I want to add another 200 amp.sub-panel in the garage, how can I connect the two? And if so what size of wire do I use? Thank's

Main Cutoffs: 200 amp outside panel feeding a 200 amp inside circuit breaker panel. [ 1 Answers ]

Would you please clarify an answer you gave to a previous question? Your answer makes me wonder about the capacity of the main shut-off circuit breaker in an inside circuit breaker panel. Is the inside circuit breaker panel the same as what you call a subpanel? Here's the question and answer:...

Adding 120 amp tankless to 200 amp panel [ 2 Answers ]

I have a 200 amp panel for an apartment with separate service from the rest of the house. I want to add an electric tankless water heater. Here's the one I'm looking at buying: Stiebel Eltron Electric Tankless Water Heater - 28/21.6 kw - 120 Amp - 240 Volt - Tempra 29 Plus Just to give you...

Adding another panel from a 200 amp service panel [ 3 Answers ]

Hi everyone, this is my first post. I have a 60 x 100 ft shop that has a 200 amp service fed in from the pole. Well I added a living space in the shop, which is about 720 sq ft. I plan on doing all the wiring myself and need a little advice on what kind of panel I should use? The living quarters...

? Adding a pool filter to a 200 amp panel [ 2 Answers ]

I have a 200 amp service and would like to add a pool filter. 2400 sq ft living space, my panel has 25 of 40 slots in use do I need additional panel, I'm trying to get a good idea of my needs prior to getting price quotes.


View more questions Search