My 200 amp Square D 40 breaker panel is full. Can I add a second 200 amp Square D panel that I already have as a sub?
![]() |
My 200 amp Square D 40 breaker panel is full. Can I add a second 200 amp Square D panel that I already have as a sub?
No. The branch circuit breaker limitation is most likely 100 or 125A.
You can feed the 200A panel with a 125A breaker but I advise against it. A 40 space panel as a sub might be too tempting to over load.
If I understand, there are two ways to handle this.
Add a sub feed lug kit to the main panel and run wire to a main lug panel (sub panel 125a as you recommended? Or
Pull two breakers from the main panel and replace them with a double power transfer breaker then run wire from the breaker to the sub panel.
Am I correct, off base or need to add something?
I should add that I have already doubled up on two breakers in the main panel and need the sub to eliminate that and add an outdoor fan and outlets to a gazebo. I'm sure more add ons are in the future.
Thanks for your help Stanfortyman.
Have you condidered having a "calculated load" completed to see if your residence is adequatley serviced. You may want to up your service to 300 amp and use a dual meter to feed both the residence's main service and the secondary panelboard.
Are you really suggesting a second meter to feed a sub-panel inside a residence?Quote:
Have you condidered having a "calculated load" completed to see if your residence is adequatley serviced. You may want to up your service to 300 amp and use a dual meter to feed both the residence's main service and the secondary panelboard.
That is not a load calculation, and really is not an indication of demand load.Quote:
My average daily usage is 38kwh or about 4 per hour.
200amp service should be adequate for that. Correct?
A real load calculation would be required.
Unless the home is really big, like 3500 sq/ft+, and/or uses electric heat or a whole house on demand water heater, a 200A service should be more than adequate.
Just adding a sub-panel does not add load. It's what you put in it that does.
Why do you need another 200A panel? Just because you have it on hand?
Personally I would not add a sub-feed lug kit to add a 200A panel to a 200A main panel. If you really need that much space then you actually may fit the description above requiring a 320/400A service.
Thanks. I realize that a load calculation is the way to go. I was just trying to show that the demand is not that heavy.
The home is about 2500 sq. ft. with oil heat. 4 beds 3 baths. The larger draws would come from the furnace/ac, through wall heat/ac unit in garage, well pump, normal 220 appliances and 220 shop tools. All the 110 is standard for this size house.
There is also a 45kw whole house automatic backup generator tied to the system.
What does that mean?Quote:
I should add that I have already doubled up on two breakers in the main panel
Sound to me like all you need to do is replace 4 regular breakers with 4 twin or slim line or piggy back breakers. That would allow you correct the doubled up breakers and give you two additional breakers for the circuits you need.