Ask Experts Questions for FREE Help !
Ask
    pjbish's Avatar
    pjbish Posts: 1, Reputation: 1
    New Member
     
    #1

    Oct 21, 2012, 03:55 PM
    Wire gauge feed 200amp panel
    What is the typical wire gauge used to feed a 200amp residential panel?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Oct 21, 2012, 04:41 PM
    4/0AL or 2/0CU
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #3

    Oct 27, 2012, 11:00 AM
    3/0 copper is 200A wire

    2/0 is 175A---too small
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Oct 27, 2012, 12:54 PM
    3/0 copper is 200A wire

    2/0 is 175A---too small
    Are you serious?
    You did see that the OP states "residential panel", right? And since it is 200A I highly doubt it is a sub-panel.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #5

    Oct 27, 2012, 01:05 PM
    Quote Originally Posted by stanfortyman View Post
    Are you serious?
    You did see that the OP states "residential panel", right? And since it is 200A I highly doubt it is a sub-panel.
    Sho nuff, though I DID type 175A when I meant THHN which is 195A, 195 ain't 200 even if it wasn't a residential panel
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Oct 27, 2012, 01:18 PM
    Wow, are you an electrician?

    Ever hear of 310.15(B)(6) in the 2008 and earlier NEC?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Oct 27, 2012, 01:19 PM
    Table 310.15(B)(7) in the 2011.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #8

    Oct 27, 2012, 01:41 PM
    Quote Originally Posted by stanfortyman View Post
    Wow, are you an electrician?

    Ever hear of 310.15(B)(6) in the 2008 and earlier NEC?
    Yeah, bud. I AM an electrician, I used the ampacity tables (table 310.16), not the "permitted' table exclusive to residential services like you did.
    That's fine if you're going to take an anonymous poster's word ( who doesn't know how to look it up) that it is a residential service.
    Also I take into account that people read this stuff that aren't electricians and may think that 2/0 is OK for ANY 200A feeder... which it's NOT.
    And there is also the difference between a good job and going for the absolute minimum like a hack does.

    So before you question my answer you might try thinking like a grownup, I didn't question how long you may have been doing this or what the EXTENT of your experience might be either, did I? I don't get all my answers out of books.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Oct 27, 2012, 03:44 PM
    Whoa, easy there little boy. All I asked was if you were an electrician.

    And yes, when a poster asks about a residential service I tend to believe them that it is indeed a residential service they are asking about. Especially on a forum called 'Home > Home & Garden > Electrical & Lighting'. If they misapply this to a commercial job that is not my problem.

    310.16(B)(7) is not only the 'permitted' table for sizing residential service conductors, it is THE table to use for sizing residential service conductors. It's not that anyone who uses that is a hack, it's that if you are not you are a fool!
    Also, if you think using 310.16(B(7) is 'hack' because it is the 'absolute minimum' then you are also an elitist who thinks unnecessarily over-building a job somehow makes you better. I guaranty you, you are not.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What gauge of wire do I use from a main panel to the sub panel [ 3 Answers ]

I am planning on adding a sub panel to my workshop where I plan on having a 20 amp breaker for the air compressor, another for the window AC unit, and a 15 amp for 6 outlets and another 15 amp for 3 fluorescent lights. I plan on running the wire from the main panel to the sub panel through conduit...

200amp main panel with 200amp sub panel [ 6 Answers ]

Hi - I'm in Colorado and about to do an electrical service panel upgrade along with a sub panel install. (I should note here that I am an electrician - Australian, so the rules I'm used to are different here in the US). I've applied for and received the relevant permit from the city, but...

Connecting large gauge aluminum wire to service panel [ 2 Answers ]

I've completed a beautifully (inspector approved) installation of a new 200 amp service panel to my home (upgraded from 100 amp). I have now strung a 0/0 underground aluminum cable in sched. 80 conduit from my barn to the main panel to connect a sub-panel in my barn to this new 200 amp panel. ...

Sub panel feed wire gauge [ 1 Answers ]

I am adding a sub panel to a new garage addition. New 125 amp panel with a double 50 amp breaker in the existing panel. The new sub panel will be 75 feet from the existing main panel. My concern is the correct wire gauge because of the length of the run. The cable will be inside underfloor then in...


View more questions Search