    What gauge of wire do I use from a main panel to the sub panel
    I am planning on adding a sub panel to my workshop where I plan on having a 20 amp breaker for the air compressor, another for the window AC unit, and a 15 amp for 6 outlets and another 15 amp for 3 fluorescent lights. I plan on running the wire from the main panel to the sub panel through conduit around the base of the house for approximately 40 feet. What type of wire should I use?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Oct 26, 2010, 09:00 PM
    The wiring size depends on what breaker you decide to feed the sub panel with... IE... a 60 amp breaker would require #6 copper wire. Are you aware of the grounding requirements for a sub-panel and the type of panel to use? Are you going to have less than 6 breakers in this panel?
    AZDesertRat's Avatar
    AZDesertRat Posts: 3, Reputation: 1
    New Member
     
    #3

    Oct 28, 2010, 05:52 PM
    I will be sinking an 8' copper rod and grounding the sub-panel to it. I will be running a total of 5 breakers so a 60 amp breaker at the main panel and #6 wire should work.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Oct 28, 2010, 06:23 PM

    Just an FYI, if you run electricity out to your shop, you must install a light outside the entrance door.

    Also, all receptacles in the garage must be GFCI protected and I strongly suggest that you use 20 amp for your receptacles, not 15 amp.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub panel load size from main panel 200 amp to 100sub 350 ft [ 1 Answers ]

Wire conduit size fromm a main 200 amp panel to a 100 amp sub panel 350 ft away

Hot wire in main panel [ 3 Answers ]

I have a rental home that I am remodeling I had all the wiring replaced by an electrician. I noticed a 20amp breaker was tripped so I replaced it with a new one and it tripped also so I took the black 12gauge wire off the breaker and its white partner, just out of curiosity I tested the wire and...

Connecting large gauge aluminum wire to service panel [ 2 Answers ]

I've completed a beautifully (inspector approved) installation of a new 200 amp service panel to my home (upgraded from 100 amp). I have now strung a 0/0 underground aluminum cable in sched. 80 conduit from my barn to the main panel to connect a sub-panel in my barn to this new 200 amp panel. ...

Sub panel feed wire gauge [ 1 Answers ]

I am adding a sub panel to a new garage addition. New 125 amp panel with a double 50 amp breaker in the existing panel. The new sub panel will be 75 feet from the existing main panel. My concern is the correct wire gauge because of the length of the run. The cable will be inside underfloor then in...