    Heil 5000 HVAC
    I have a Heil 5000 central air unit. The compressor or the unit it outside keeps tripping the breaker. If I let it set for a few hours, then I can reset the breaker and it will run just fine and cool the house. But after a while, a few hours I'm guessing, it will trip the breaker. Although I have not had the time to sit around and babysit it to see actually when the breaker is tripping, I have a hunch when it is. Now I am not very familiar with AC units, I am rather mechanically and electrically inclined. If I am correct these compressor work with the same principle as a regular air compressor, when they start a pressure relief valve is activated so that the motor can start and come up to full running speed before the compression actually starts. I did a little research and discovered that this compressor requires a minimum circuit ampacity of 25.5 amps. The wiring and circuit breaker was 10 awg on a 30 amp breaker. Now if you take into consideration the rules of electrical theory, you are required to be about the circuit ampacity by 20%. Whichc would mean that 10 AWG and a 30 amp breaker is not sufficient. Now let me state that the compressor is requires 90 feet of conductor to get from the breaker panel to the compressor disconnect. I believe that I may have an issues with what I believe should be the pressure relief valve for start. Like I said, if I let it set for a while, I can reset the breaker and it will run fine. I believe that letting it set for a while allows the pressure to bleed of the high pressure side allowing it to start much easier and run properly.

    Ok so that was a quick version of my issue. I welcome all and any input.

    Thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Aug 10, 2012, 04:25 PM
    You can't relieve pressure without releasing Freon.
    Many AC Techs or systems will have a delay so the compressor doesn't try to start with high head pressure, the delay helps.
    I would use an Amprobe to see the current, could be a bad breaker or loose connections on the breaker or breaker buss.
    Buckslayer9000's Avatar
    Buckslayer9000 Posts: 6, Reputation: 1
    New Member
     
    #3

    Aug 10, 2012, 04:47 PM
    Ok so I forgot to mention that since I believe according to electrical theory that the conductor and bresker are too small I did replace the conductor and breaker. There is now new 6awg aluminum range cable for the conductor and a new 40 amp breaker and it still trips. I did use an amprobe bef
    Buckslayer9000's Avatar
    Buckslayer9000 Posts: 6, Reputation: 1
    New Member
     
    #4

    Aug 10, 2012, 04:50 PM
    Anmprobe and before I replaced the conductor and breaker it was pulling 110amps for the first 5 seconds and then would drop to it's normal running which was 15 to 16 amps. But that was only after I let it set for a while
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Aug 10, 2012, 05:41 PM
    Quote Originally Posted by Buckslayer9000 View Post
    Anmprobe and before I replaced the conductor and breaker it was pulling 110amps for the first 5 seconds and then would drop to it's normal running which was 15 to 16 amps. But that was only after I let it set for a while
    Put a hard start kit on it and while you are at it check the run capacitor for the proper value. Many times a run capacitor will become weak from use or age and the run capacitor can be a cause of your type of problems.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Aug 10, 2012, 05:43 PM
    Likely a Compressor problem, you may get lucky and have bad connections or a bad capacitor.
    Buckslayer9000's Avatar
    Buckslayer9000 Posts: 6, Reputation: 1
    New Member
     
    #7

    Aug 10, 2012, 07:33 PM
    Ok awesome input. I have been pondering capacitor issues but I'm not sure what the value of these capacitors should be. I'm well aware of how to test them. But like I said, I just don't know what the value should be. Could you point me in that direction?
    Buckslayer9000's Avatar
    Buckslayer9000 Posts: 6, Reputation: 1
    New Member
     
    #8

    Aug 10, 2012, 07:34 PM
    Oh yeah definitely not a connection issues... I have checked that like 10 times because I keep questioning myself
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #9

    Aug 10, 2012, 08:18 PM
    Quote Originally Posted by Buckslayer9000 View Post
    Oh yeah definitely not a connection issues...... I have checked that like 10 times because I keep questioning myself
    On the Compressor itself?
    Buckslayer9000's Avatar
    Buckslayer9000 Posts: 6, Reputation: 1
    New Member
     
    #10

    Aug 10, 2012, 08:25 PM
    On every connection even related to the compressor

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a heil, 5000 central heat unit , doesn't staying running? [ 0 Answers ]

I have a neil 5000, heating unit, it comes on and shuts off after a bit ! A fan in it runs none stop, can anyone help with this question ?

Have older model Heil HVAC the fan blower works on heat but not on cool . [ 1 Answers ]

We have tried everything .Cleaned the coils on the outside unit , changed the thermostat and still the inside fan does not blow on cool but it works perfectly fine on heat .We also tried fan only and that didn't work either .

Heil 5000 model# ntc5050bea1 [ 1 Answers ]

Were you able to find the schematic given the s# & m# of a HEIL furnace?

Heil 5000 High Efficiency air-conditioner will not cool. [ 2 Answers ]

Hello, Florida summers at 95-degrees are terrible, especially when your air-conditioner stops working in the middle of it. :mad: Here are the symptoms: - It's connected to a gas line. The heat works well, but when the cooling is turned on it blows out room-temperature air. - The fan on...