I have a Heil 5000 central air unit. The compressor or the unit it outside keeps tripping the breaker. If I let it set for a few hours, then I can reset the breaker and it will run just fine and cool the house. But after a while, a few hours I'm guessing, it will trip the breaker. Although I have not had the time to sit around and babysit it to see actually when the breaker is tripping, I have a hunch when it is. Now I am not very familiar with AC units, I am rather mechanically and electrically inclined. If I am correct these compressor work with the same principle as a regular air compressor, when they start a pressure relief valve is activated so that the motor can start and come up to full running speed before the compression actually starts. I did a little research and discovered that this compressor requires a minimum circuit ampacity of 25.5 amps. The wiring and circuit breaker was 10 awg on a 30 amp breaker. Now if you take into consideration the rules of electrical theory, you are required to be about the circuit ampacity by 20%. Whichc would mean that 10 AWG and a 30 amp breaker is not sufficient. Now let me state that the compressor is requires 90 feet of conductor to get from the breaker panel to the compressor disconnect. I believe that I may have an issues with what I believe should be the pressure relief valve for start. Like I said, if I let it set for a while, I can reset the breaker and it will run fine. I believe that letting it set for a while allows the pressure to bleed of the high pressure side allowing it to start much easier and run properly.
Ok so that was a quick version of my issue. I welcome all and any input.
Thanks