Ask Experts Questions for FREE Help !
Ask
    bubby2's Avatar
    bubby2 Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 2, 2012, 06:35 AM
    Nfpa 70
    What is the nfpa on warehouse lighting
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Jul 2, 2012, 08:41 AM
    Please explain your question in more detail...
    For typical warehouse lighting the NFPA has no requirements. Any requirements
    Would come first from the Building Code with possible recommendation from the IESNA.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jul 3, 2012, 10:35 AM
    The only reference in NFPA 70 regarding lighting is to allow for .25 VA per square foot as a minimum load of general lighting, and to use the first 12,500 VA at 100% when doing load calculations.

    If you would answer Hfcarson's question and provide more detail, perhaps we can provide a better answer.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical nfpa 70 sizing of ac equipment wire and breaker size [ 2 Answers ]

Ac equipment. Minimum circuit ampacity is 18 amps max is 40. What size wire and what size breaker?

What does nfpa 70 type ITC refer to? [ 1 Answers ]

What does nfpa 70 type itc refer to?

Reading the NFPA 70 etc. National Electric Code Online [ 1 Answers ]

It does seem impossible to search for, but just about any code published by the NFPA is readable online. You will have to register for a username and password. The NFPA 70: National Electrical Code starts here: NFPA 70: National Electrical CodeŽ Near the bottom af the page there is a...

Stand Pipe refers to which one in NFPA [ 0 Answers ]

Hi All, When I read NFPA, instead of getting answer I get more confused , As I know there will be several risers in fire System like Sprinkler Riser , Riser Serving Fire Hose Cabinet , and riser Srving Landing Valve. In NFPA , Stand Pipe Refers to which Riser? I would be thankful if someone...


View more questions Search