Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Nfpa 70 (https://www.askmehelpdesk.com/showthread.php?t=677881)

  • Jul 2, 2012, 06:35 AM
    bubby2
    Nfpa 70
    What is the nfpa on warehouse lighting
  • Jul 2, 2012, 08:41 AM
    hfcarson
    Please explain your question in more detail...
    For typical warehouse lighting the NFPA has no requirements. Any requirements
    Would come first from the Building Code with possible recommendation from the IESNA.
  • Jul 3, 2012, 10:35 AM
    tkrussell
    The only reference in NFPA 70 regarding lighting is to allow for .25 VA per square foot as a minimum load of general lighting, and to use the first 12,500 VA at 100% when doing load calculations.

    If you would answer Hfcarson's question and provide more detail, perhaps we can provide a better answer.

  • All times are GMT -7. The time now is 11:06 PM.