    Can THHN Wire be used in PVC under ground.
    Can THHN Wire be used in PVC under ground.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Dec 17, 2011, 01:26 PM
    No, THHN is listed (Article 300, Table 310.13(A)) as dry or damp areas.

    Earth is considered a wet area. Conduit, below ground level is also considered to be in a wet area.

    THHW, THW, THW-2,THWN, THWN-2 and TW are acceptable for wet areas.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Dec 17, 2011, 02:12 PM
    Check the wire you may have, most THHN is dual rated as THHN/THWN

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is THHN and THWN wire rated for cable tray use? If not what wire should be used? [ 6 Answers ]

Is THHN and THWN wire rated for cable tray use? If not what wire should be used in cable tray in utility chase for apartment building?

Thhn wire [ 5 Answers ]

Can thhn stranded wire be connected to circuit breakers in a electrical panel. What are the pro and cons (if there are any)? Thanks

# of thhn through pvc [ 1 Answers ]

How many # 8 can you pull through 3/4 and how many # 6 in a 1''

Thhn/Thwn Wire [ 3 Answers ]

What's the difference in THHN/THWN besides the W for wet locations. Are these one in the same wire? I see it advertised as such. Sometimes with and with out the THWN part. Just really curious about this M


View more questions Search