Ask Experts Questions for FREE Help !
Ask
    ejppbsj's Avatar
    ejppbsj Posts: 1, Reputation: 1
    New Member
     
    #1

    Mar 4, 2010, 12:59 PM
    Is THHN and THWN wire rated for cable tray use? If not what wire should be used?
    Is THHN and THWN wire rated for cable tray use? If not what wire should be used in cable tray in utility chase for apartment building?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 4, 2010, 01:22 PM
    Yes, you can use THHN/THWN wire in cable tray.

    See :
    http://www.southwire.com/support/THH...ifications.htm
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Mar 6, 2010, 06:08 AM
    It did occur to me, if you had to ask this question , you probably should be reviewing Article 392 of the NEC, as cable tray has special requirements for installing wire in cable tray, such as bundling feeder conductors, spacing between bundles, changes to ampacity of wire, etc.
    Lance moreau's Avatar
    Lance moreau Posts: 1, Reputation: 1
    New Member
     
    #4

    Aug 16, 2011, 06:50 AM
    Can 500mcm thhn be run in single conductor runs in a cable tray indoor for a service
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Aug 17, 2011, 02:40 AM
    Yes , see,


    Quote Originally Posted by tkrussell View Post
    Article 392 of the NEC, as cable tray has special requirements for installing wire in cable tray, such as bundling feeder conductors, spacing between bundles, changes to ampacity of wire, etc.
    barneyc44's Avatar
    barneyc44 Posts: 1, Reputation: 1
    New Member
     
    #6

    Jan 14, 2013, 05:54 AM
    Can THHN cabling be used for UPS batteries and in cable tray?

    This application is from the battery disconnect to the battery terminals.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Jan 15, 2013, 06:46 AM
    Yes.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Thhn wire [ 5 Answers ]

Can thhn stranded wire be connected to circuit breakers in a electrical panel. What are the pro and cons (if there are any)? Thanks

Best for underground conduit. Thw vs thwn wire? [ 6 Answers ]

I am putting in about a 60' pvc conduit underground. It is a very wet location. I was going to use the wire with the thick insulation. The sales people at the hardware stores wanted to sell me thwn. They said it was better. They did not have the the. I understand the thwn has a jacket coating...

Thhn/Thwn Wire [ 3 Answers ]

What's the difference in THHN/THWN besides the W for wet locations. Are these one in the same wire? I see it advertised as such. Sometimes with and with out the THWN part. Just really curious about this M

Free wire THHN [ 2 Answers ]

I have been looking in the NEC and can't seem to find the code which states whether THHN can be free wired for low voltage wiring? Anyone Know?

Running THHN wire above 8 feet. [ 3 Answers ]

I am wiring a barn/shop area and have run all wiring in EMT conduit except above 8 feet where I have run some ROMEX to lights. My question is: I need one extra wire for a 3-way switch traveler wire. Can I staple this along side of the ROMEX wire above 8' in the hi bay area, or does it have to be in...


View more questions Search