-   -   Can THHN Wire be used in PVC under ground. (https://www.askmehelpdesk.com/showthread.php?t=620404)

  • Dec 17, 2011, 01:14 PM
    guest598
    Can THHN Wire be used in PVC under ground.
    Can THHN Wire be used in PVC under ground.
  • Dec 17, 2011, 01:26 PM
    donf
    No, THHN is listed (Article 300, Table 310.13(A)) as dry or damp areas.

    Earth is considered a wet area. Conduit, below ground level is also considered to be in a wet area.

    THHW, THW, THW-2,THWN, THWN-2 and TW are acceptable for wet areas.
  • Dec 17, 2011, 02:12 PM
    tkrussell
    Check the wire you may have, most THHN is dual rated as THHN/THWN