    Breaker size
    A circuit that pulls 19 amps,what size breaker would I need
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 1, 2011, 03:36 AM
    Generally most circuits need to be sized 125% of the load, would need a 30 amp breaker with #10 wire.

    What is the type of load on this circuit?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Dec 1, 2011, 04:59 AM
    I'd have to disagree with the "most" part.
    Some circuits do, but in a residence very few are, or must be, considered a continuous load and need the 125% multiplier.

    Before giving a firm answer I'd have to ask the same question as TK. It all depends on what the circuit is being used for.
    If it is for an appliance with a standard 20A plug attached it cannot be on a 30A circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size breaker can I use? [ 2 Answers ]

Hi, I am in the Philippines and they use a 2 wire (black & white - No Ground)- 220 Volt system. I brought from home (US) some 12-2 wire and want to install 3 outlets for "window type" air conditioner units one that is 720W and the other 2 have not been bought. Neither one will be bigger than this...

What need to the size of breaker [ 0 Answers ]

Hi All, I’m designing communication racks that include IBM servers and other communication equipment. The input power is -48vDC and the total (maximum) of watt is 29466W. Can someone help with 2 questions: 1. What is the size of cable in need to use here (AWG wire size)? 2. What need to be the...

Breaker size [ 2 Answers ]

I have a 7.5 hp motor that was wired 480 volts 3 phase rated at 14 amps and I need to change from 480 volts down to 208 volts. What would the breaker size need to be rated for at that voltage.

Compatibilities between awg wiring, breaker amp size, outlet amp size [ 4 Answers ]

Hi. Is there a resource out there, prefereably on the web, that outlines the compatibilities between awg wiring, the breaker amp size, outlet amp size, how many recepticles/outlets can be on x amp outlet, etc? For example, it would be nice to see something that shows: you can use a 20 amp...


View more questions Search