  • Nov 30, 2011, 11:39 PM
    terry1973
    Breaker size
    A circuit that pulls 19 amps,what size breaker would I need
  • Dec 1, 2011, 03:36 AM
    tkrussell
    Generally most circuits need to be sized 125% of the load, would need a 30 amp breaker with #10 wire.

    What is the type of load on this circuit?
  • Dec 1, 2011, 04:59 AM
    stanfortyman
    I'd have to disagree with the "most" part.
    Some circuits do, but in a residence very few are, or must be, considered a continuous load and need the 125% multiplier.

    Before giving a firm answer I'd have to ask the same question as TK. It all depends on what the circuit is being used for.
    If it is for an appliance with a standard 20A plug attached it cannot be on a 30A circuit.