    Symptoms are; burners ignite and after a short time they shut off. The blower never
    Symptoms are; burners ignite and after a short time they shut off. The blower never comes on. If I turn the blower to full-time on, the heat works fine. Should the module have 24 vac when the blower is full-time on (it does)? I believe the control module is bad.

    Do I check the 24 vac voltage when the unit is set to auto to determine if the module is bad?
    JonesHVAC's Avatar
    JonesHVAC Posts: 173, Reputation: 12
    Junior Member
     
    #2

    Oct 11, 2011, 06:14 PM
    In theory the 24vac has nothing to do with the blower motor other than it is needed in pre heating sequences in order for the blower to come on... for ex: thermostat calls for heat --> closes circuit completing 24vac to control board, series of events within control board --> inducer motor comes on expelling any gases in exhaust --> ignitor glows --> gas valve opens --> flames --> limit opens --> blower comes on. There are some other steps in there but are not needed for this.

    Turn thermostat off and shut power down. Clean your flame sensor with a piece of fine grade sand paper careful not to break it. It is the little probe looking thing up near the burners. Turn power back on and turn thermostat back on to call for heat. Let me know how that works out for you.
    tbeale's Avatar
    tbeale Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 14, 2011, 05:06 AM
    The Heil Fan Control Timer was bad.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Burners ignite and stay on, blower does not? [ 2 Answers ]

I have a Rheem RRPLB024JK08E outdoor gaspack, 5 months. Old. It locked itself out, red lights indicate high limit open. Put in new high limit switch, no change. After I reset it (kill power) it works fine for about 8 or 10 cycles. Then, draft inducer comes on... burners ignite and stay on, but no...

My furnace burners shut off after burning for a very short period? [ 0 Answers ]

I have an 10 year old armstrong natural gas furnace which goes through the ignition cycle, everything seems fine for a few seconds, then the burners shut off. I have tried cleaning the flame sensor, didn't work. So then I replaced flame sensor- same problem. I just looked at the pressure sensor,...

Heil 7000 furnace, blower stays on and burners don't ignite [ 14 Answers ]

Furnace Info: -Upflow Condensing Gas Furnace is a Heil 7000 (model# NUGK075DG09) -Electric spark or host surface ignitor ( I think it's spark) -Installed Oct. '96 (when we built the house) -90% efficiency -wall thermostat is honeywell programmable. Don't know model but was also purchased in...

Burners ignite then shut of unexpectedly. [ 1 Answers ]

Age of equipment: 5 Years Brand (Manufacturer): RUUD Silhouette II Efficiency: 80% Natural gas, Induced-Draft Blower Furnace only inside unit What does it do? Not do? First thought it was the thermostat and replaced it but am still having intermittent igniting of the burners. If I turn...


View more questions Search