    WHat size of Wire and breaker need for a shed
    I built a Shed 30 x 20 . The location is at approximately 150 to 180 feet away from the main building electric box. I will have three switches, three outlets and 4 fluorescents (each with 4 bulbs) light fixture, with a #14 wire. Beside I will have three outlets for a work shop by the counter top table with #12 wire. I Am planing to run an AC floor unit while I am working there. Maybe I will install a vacuum system while I do cuttings. It will be OK if I set a 3/4" gray pipe to run two circuits #14 and #12 wires on a two separate breakers with 15 and 20 amps? Or I can run #8 wire on a 40 amps breaker to a sub-panel in the shed and two or three brakers (15amp, 20 amps) in sub-panel? Please help with some answers it will be appreciated it. Thanks. JJ
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 9, 2011, 04:46 AM
    Due to the size of the shed and the potential to have some decent motor loads, and the distacne, I would install #2 - 4 wire aluminum URD cable, which can be direct buried, to eliminate voltage drop.

    You may sleeve the URD cable with 2 inch PVC conduit for added protection if the soil is rocky, and will allow the cable to be replaced or upgraded later with no excavating.

    Your plan of running only # 14 and/or #12 that distance will not work at all.

    Without knowing exactly amp or wattage load of the motors, I suspect #8 copper will not be sufficient either.

    Aluminum wire is much cheaper than copper, and when sized and terminated properly, works just as well as copper.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size breaker for 6/3 wire for 100ft [ 6 Answers ]

I have a 250 ft run and I came across a 100 ft of 6/3. I want to run the 6/3 from temp pole to another box. Then use existing wire the rest of the way. What size breaker should I use at temp pole?

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

What wire size, and breaker rating do I need. [ 21 Answers ]

I am looking to add power to my out building. It is 100/120ft from the main service box. The service box is a 200a service, and the total of the breaker installed is 230. There are plenty of extra slots for breakers to be added. I am wanting to run 2circuits to the building. #1 will operate 2...

Wire and Breaker size [ 2 Answers ]

I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?