    What size breaker for 6/3 wire for 100ft
    I have a 250 ft run and I came across a 100 ft of 6/3. I want to run the 6/3 from temp pole to another box. Then use existing wire the rest of the way. What size breaker should I use at temp pole?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 5, 2010, 09:32 AM

    J,

    It does not work that way. Temporary wiring is just that. It cannot be used as permanent wiring. Also, we need much more information from you.

    For example, what is the Type of the cable? That gates how cable can be used. Does the cable have Copper or Aluminum conductors. At a hundred feet #6/3 AWG Copper can handle up to 60 Amps, depending on what it is connecting to. You need to know the temperature of the connection point to select the correct amperage. For example, 310.16 divides the temperature into 3 categories, 60c - 75c - 90c. The column you use is the column that gives the rating of what you are connecting to. That in turn gives you the max amperage you can supply via the cable.

    Are you making an Overhead Connection or a Lateral connection (below ground)?
    jdooley5517's Avatar
    jdooley5517 Posts: 6, Reputation: 1
    New Member
     
    #3

    Aug 5, 2010, 04:13 PM
    How about I just go with a 50 and call it good. And its being run underground. Oh and it copper
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Aug 5, 2010, 05:27 PM

    J,

    That's part of the info we need.

    For 6/3 AWG copper it is 55 Amp. (Using the 60c column) because you do not know the termination temp of the circuit, we have to use the 60c column.

    Since we do not know what type of cable you have, I do not know if it can be buried, only certain types of cable can be direct buried or has to be used in conduit. Nor do I know if the cable can be put into conduit. This affects the depth of the required trench.

    Can you give me something more to work with?

    Obviously, if you were able to wire your Bat Cave you must be able to give us some more info. :)
    jdooley5517's Avatar
    jdooley5517 Posts: 6, Reputation: 1
    New Member
     
    #5

    Aug 5, 2010, 07:45 PM

    It's a 6/3 wg type ufb copper wire. And I've had lights in the bat cave for 12 years now on a temp pole
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Aug 6, 2010, 10:42 AM

    J,

    Is there a secret passage into the Bat Cave, one an electrical inspector cannot find. I am concerned about the use of a temporary pole. I mean, 12 years is an awful long time for a temporary situation.

    As to the cable, South Wire markets a 6/3 UF-B cable. It is suited for direct-burial, which means that is needs to be covered over by at least 18" of top cover.

    Since I have no idea what the connection temp rating of the device you are wiring up, it is necessary to use the 60c column.

    Translated, that means that according to the NEC 2008, Chapter 3, article 310.16 the max amperage that can be used is 50 amps or a maximum of 40 Amps on a continious usage cable.

    Continuous Load is rated at 125% of load. For example, a 32 amp continious load will be sized at 40 amps. 32A X 1.25 = 40A.

    If you use the 50A load, then you would need to replace the entire cable with #4 AWG because the rating of the cable is exceeded.

    50A X 1.25 = 62.5 Amps (rounded up to 63 Amps)
    jdooley5517's Avatar
    jdooley5517 Posts: 6, Reputation: 1
    New Member
     
    #7

    Aug 6, 2010, 07:19 PM

    Thanks for all your help that should be good

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size for 80 amp breaker [ 1 Answers ]

I am installing a 80 amp sub panel and need to know the size of the wire from the main to sub

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Wire size and breaker upgrade. [ 3 Answers ]

I am wiring up a secondary basement bathroom that calls for a saniflo saniplus toilet, motor has a 7 amp rating (to also be used for the shower). The home run is #12 to an outlet in the bathroom which branches to an outlet in the sitting room which has a freezer (5.6 amp) and a switch from the...

What wire size, and breaker rating do I need. [ 21 Answers ]

I am looking to add power to my out building. It is 100/120ft from the main service box. The service box is a 200a service, and the total of the breaker installed is 230. There are plenty of extra slots for breakers to be added. I am wanting to run 2circuits to the building. #1 will operate 2...

Wire and Breaker size [ 2 Answers ]

I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?


View more questions Search